There is absolutely no basis for evaluating the common North American electrical grounding standard as DIY ("do it yourself"). To suggest such is to assert that utilities do not do their own grounding which could not be further from the truth and neglegts the existence of PLENTY of residential split-phase services which predate modern grounding standards, were not installed to standard to begin with, or were modified because of old wives tales about "stray voltage" and "parallel paths to ground" and do NOT have their own grounding electrode connection, much as it sounds is the case in UK wiring practices.
At one time, in overhead power distribution, it might not have been uncommon for a utility to ground** the neutral of their systems maybe only as often as at one pole every five miles. Then standards were revised and it was done more frequently, maybe every mile. Today's standard is to make this grounding connection at every pole. Why the change? To ensure that zero is still zero at both the top and bottom of every pole, not just at every fiftieth or tenth pole. In order for the system to work (safely) zero has to be zero everywhere. And since transformers are quite often located remotely from the structures they serve, and said structures are often at the same potential as the Earth that surrounds and supports them, most NA utilites like to make sure that the same zero exits at the served structure as does at their transformer coil. The easiest way to ensure this is to connect them with a conductor. After this point on the wiring system the grounded conductor, so called because there has been made an intentional connection to ground on it, becomes separate from the equipment grounding conductor, a nominally non-current-carrying part of the circuit that functions as the backup path for any irregular or objectionable currents. Exactly where a grounding connection can be or is required to be physically made is a matter of regulation but it all works the same in the end.
Grounding and lightning protection are closely related but are done in somewhat different ways and electrical service grounding is not inteded to provide lightning protection specifically as its primary purpose. No conductor exists that can safely dissapate the entirety of an average lighning strike; anyone whos life was "saved" by just enough grounding as to not become a significant current path for a lightning strike is indeed quite lucky. But for a million volts, traversing thousands of feet of air, a short length of wet wooden pole and a very short length (likely 6ft or less) of buried metal connected through a puny wire to said pole some hundred or hundreds of feet away are going to look about the same. Truth is the average ground rod is an awful ground and while one is often better than nothing, two is often "just good enough."
It is my understanding that the main function of a grounding electrode system that is connected to a purpose-built lightning protection system is more or less to make the structure it is placed upon "look shorter", to help eqaualize buildup of gradients that are suspected to give rise to a lightning strike; think of it more as preventative maintenance with a lesser capacity to act as a sacrificial path in the event that lightning still does strike.
** (read: mechanically and electrically connect the circuit conductor with nominal zero potential with respect to ground to a local Earth potential)
At one time, in overhead power distribution, it might not have been uncommon for a utility to ground** the neutral of their systems maybe only as often as at one pole every five miles. Then standards were revised and it was done more frequently, maybe every mile. Today's standard is to make this grounding connection at every pole. Why the change? To ensure that zero is still zero at both the top and bottom of every pole, not just at every fiftieth or tenth pole. In order for the system to work (safely) zero has to be zero everywhere. And since transformers are quite often located remotely from the structures they serve, and said structures are often at the same potential as the Earth that surrounds and supports them, most NA utilites like to make sure that the same zero exits at the served structure as does at their transformer coil. The easiest way to ensure this is to connect them with a conductor. After this point on the wiring system the grounded conductor, so called because there has been made an intentional connection to ground on it, becomes separate from the equipment grounding conductor, a nominally non-current-carrying part of the circuit that functions as the backup path for any irregular or objectionable currents. Exactly where a grounding connection can be or is required to be physically made is a matter of regulation but it all works the same in the end.
Grounding and lightning protection are closely related but are done in somewhat different ways and electrical service grounding is not inteded to provide lightning protection specifically as its primary purpose. No conductor exists that can safely dissapate the entirety of an average lighning strike; anyone whos life was "saved" by just enough grounding as to not become a significant current path for a lightning strike is indeed quite lucky. But for a million volts, traversing thousands of feet of air, a short length of wet wooden pole and a very short length (likely 6ft or less) of buried metal connected through a puny wire to said pole some hundred or hundreds of feet away are going to look about the same. Truth is the average ground rod is an awful ground and while one is often better than nothing, two is often "just good enough."
It is my understanding that the main function of a grounding electrode system that is connected to a purpose-built lightning protection system is more or less to make the structure it is placed upon "look shorter", to help eqaualize buildup of gradients that are suspected to give rise to a lightning strike; think of it more as preventative maintenance with a lesser capacity to act as a sacrificial path in the event that lightning still does strike.
** (read: mechanically and electrically connect the circuit conductor with nominal zero potential with respect to ground to a local Earth potential)