Mean Rating Temperature for insulation in ASHRAE

1 reply · 3K views · last reply
tj00343
Messages
59
Reaction score
0
Hello,
Can someone please tell me what the mean rating temperature in the tables provided in ASHRAE fundamentals, ASHRAE standard 90.1&90.2 for chilled water insulation indicates.
 
Attachments
  • Table 6.8.3B, Minimum Pipe Insulation Thickness for cooling systems (chilled water, brine, and refrigerant), listing fluid temperature range, insulation conductivity, mean rating temperature, and thickness by pipe size in mm.
    insulation 2.PNG
    15.3 KB · Views: 530
There should be a footnote (a) below that table that may give a little context. It should say something like this (excuse the units):

a) For insulation outside the stated conductivity range, the minimum thickness (T) shall be determined as follows: T = r{(1 + t/r)K/k – 1}where T = minimum insulation thickness (in.), r = actual outside radius of pipe (in.), t = insulation thickness listed in this table for applicable fluid temperature and pipe size, K = conductivity of alternate material at mean rating temperature indicated for the applicable fluid temperature (Btu·in./h·ft2·°F); and k = the upper value of the conductivity range listed in this table for the applicable fluid temperature.