Mechanical engineer's kVA question

  • Thread starter bill nye scienceguy!
  • Start date
  • Tags
    Mechanical
In summary, The individual is seeking information on how to calculate kVA for machine tools' power consumption given variables such as volts, frequency, and phase. The power factor, which is the ratio of actual power to apparent power, is also discussed. It is noted that power factor can vary for different types of loads, with inductive loads such as motors typically having a lower power factor than resistive loads like lightbulbs. The individual also asks for clarification on the relationship between kVA and kW, and the significance of working in 1- or 3-phase. It is explained that power factor must be taken into account when calculating kVA, and that it cannot be easily calculated from first principles.
  • #1
bill nye scienceguy!
127
0
Hi all.

I'm a mechanical engineer by training and a manufacturing engineer by trade. I currently find myself in the position of being asked to fill out a spreadsheet containing, amongst other things, machine tools' power consumption in kVA.

Occasionally an OEM will be helpful and provide this directly in the datasheet but more often I'm given volts, frequency and phase. How can I reliably approximate a value for kVA given these variables or what else do I need to know in order to calculate?

Many thanks!
 
Engineering news on Phys.org
  • #2
You need to know the current that is drawn by the machine to find power.
 
  • #3
If I'm understanding the units correctly kVA is just kW, so as long as the supplier specifies the machine's power consumption you can convert to kW.
 
Last edited:
  • #4
Sorry, it's been a long day. Of course I need to know current.

I'm not entirely sure of the relationship between kVA and kW beyond that they're both measures of power. For example, in the following calculator 480kW is seen to be equivalent to 600kVA. What equation sits behind the buttons on the screen? Also, in 'power requirement calculator' it mentions something called a power factor - can someone give me a quick explanation on what this is? What is the significance of working in 1- or 3-phase wrt a difference in power?

http://dieselserviceandsupply.com/power_calculator.aspx

If it's possible to explain this without using complex numbers I'd be much obliged...
 
Last edited:
  • #5
The wiki on this is good, but in short, since AC electricity is a sine wave, if the waves for volts and amps are not aligned, you aren't multiplying peak (rms actually) volts by peak amps.

But many electrical devices are sized based on their amps and supply voltage, so you still need to know the APPARENT power and that's what kVA is.

And apparent power and actual power are related by power factor.
 
  • #6
Read this and use "Power triangle" instead of complex numbers.
http://www.allaboutcircuits.com/vol_2/chpt_11/2.html
 
  • #7
Ok, this is starting to make sense. To check my understanding: if something has a power rating of 600kVA and 480kW that means there's a power factor of 0.8? And in words that means that means that there is 600kVA total power in the system and 480kW is dissipated by the load.

Assuming I have that right, how do I calculate the power factor from first principles ie not from kW/kVA? Let's say I know that the current is 3-phase or single phase but I don't know the impedance angle.
 
  • #8
It can't easily be calculated from first principles. It has to be estimated or looked up in a table.
 
  • #9
Ok, so is it safe to assume a power factor of 0.8 in estimating kVA? I say 0.8 since this seems to be quite common.
 
  • #10
Different devices have different power factors in different situations. .8 works for a reasonably well loaded motor: inductive loads are subject to power factor, resistive loads are not.
 
  • #11
I just asked google about inductive loads and I got this.

http://www.markallen.com/teaching/ucsd/147a/lectures/lecture3/3.php

It explains that inductive loads involve magnetic fields eg in a motor. It goes on to say that resistive loads convert electrical energy into another form of energy eg in a lightbulb. So I can see that whenever I have a motor I need to take into account power factor.

This is maybe an adjunct at this point but - does this mean that in the case of a lightbulb the apparent power is equal to the dissipated power? Or is it not appropriate to view a resistive load in those terms?
 
Last edited by a moderator:
  • #12
You are correct: when power factor is 1, actual and apparent power are equal.
 

What is a mechanical engineer's kVA question?

A mechanical engineer's kVA question refers to the calculation of the kilovolt-ampere (kVA) rating for a mechanical system. This is an important measurement for determining the system's power requirements and ensuring it is properly designed and functioning.

Why is the kVA rating important for mechanical engineers?

The kVA rating is important because it helps mechanical engineers determine the appropriate size and capacity of electrical equipment needed for a system. This includes motors, transformers, and other devices that require a certain amount of power to operate efficiently.

How is the kVA rating calculated?

The kVA rating is calculated by multiplying the voltage (V) by the current (A) and dividing the result by 1000. This is represented by the formula kVA = (V x A) / 1000. It is important to note that this calculation only applies to AC (alternating current) systems.

What factors can affect the kVA rating for a mechanical system?

Several factors can affect the kVA rating for a mechanical system, including the type of load, power factor, and voltage drop. The type of load refers to whether the system is resistive, inductive, or capacitive. The power factor is a measure of how efficiently the system is using the electricity it receives. Voltage drop occurs when there is a decrease in voltage as electricity travels through wires and other components.

How can mechanical engineers ensure the kVA rating is accurate for a system?

To ensure the kVA rating is accurate for a system, mechanical engineers should carefully consider all of the factors that can affect it and make accurate measurements of voltage and current. They may also consult with electrical engineers to confirm their calculations and ensure the system is properly designed and functioning.

Similar threads

Replies
13
Views
2K
  • STEM Career Guidance
Replies
19
Views
2K
  • STEM Academic Advising
Replies
5
Views
1K
Replies
2
Views
77
Replies
6
Views
4K
  • Mechanical Engineering
Replies
3
Views
3K
  • STEM Academic Advising
Replies
6
Views
1K
  • STEM Career Guidance
Replies
5
Views
2K
  • General Engineering
Replies
8
Views
14K
Replies
3
Views
526
Back
Top