Negative Voltage Regulation in Transformer

Click For Summary
SUMMARY

The discussion centers on the phenomenon of negative voltage regulation in transformers, specifically how a leading power factor can lead to this occurrence. Participants highlight that capacitance across the secondary terminal can counteract leakage reactance on the primary side, resulting in an increased primary and secondary voltage. The confusion arises from calculations regarding full load and no load voltages, particularly in the context of transformer voltage regulation examples. Clarifications on these calculations are necessary for a comprehensive understanding of the topic.

PREREQUISITES
  • Understanding of transformer operation and voltage regulation principles
  • Knowledge of power factor concepts, especially leading power factor
  • Familiarity with phasor diagrams in electrical engineering
  • Basic skills in electrical calculations related to transformers
NEXT STEPS
  • Research "Transformer Voltage Regulation Calculations" for detailed methodologies
  • Study "Leading Power Factor Effects on Transformers" to understand implications
  • Examine "Phasor Diagrams in Electrical Engineering" for visual representation techniques
  • Explore "Capacitance in Transformer Design" to learn about secondary terminal effects
USEFUL FOR

Electrical engineers, power system analysts, and students studying transformer theory and voltage regulation will benefit from this discussion.

QwertyXP
Messages
66
Reaction score
0
How can a transformer have negative voltage regulation?
A few texts state that a leading power factor can give rise to negative power factor, but I have not been able to figure out how this is possible.

One vague explanation in my mind is that capacitance across the secondary terminal will somehow cancel out the leakage reactance on the primary side, thus resulting in a higher primary voltage and hence higher secondary voltage as well.

Can somebody please describe more accurately.
 
Engineering news on Phys.org
I think I've somewhat become used to the idea of negative voltage regulation after going through lots of articles and also drawing the phasor diagram myself. The main issue seems to be resolved now.

However, I still have confusions as far as the related calculations are concerned. For example, if you have a look at the following link:
http://yourelectrichome.blogspot.com/2011/07/voltage-regulation-of-transformer.html

According to example 1, full load current = KVA rating/secondary voltage specified in the question statement. Thus in this case, he has assumed 125V to be the full load voltage. However, in another place (part ii), he considers 125V to be the no load voltage while calculating the secondary terminal voltage.

Is this a mistake, or did he make this assumption because the value of current would not differ by too much even if no load voltage were used in the calculation?
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
Replies
8
Views
2K
Replies
2
Views
3K
  • · Replies 16 ·
Replies
16
Views
4K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 9 ·
Replies
9
Views
2K
Replies
64
Views
8K
Replies
6
Views
4K
Replies
2
Views
2K
  • · Replies 36 ·
2
Replies
36
Views
12K