Overhead transmission line protection failure

  • Thread starter Tee
  • Start date
  • #1
Tee
8
0

Main Question or Discussion Point

Hello everyone ,

I am still new to the protection field so i would appreciate if you can help me with analysis of the following,

A 13.8 Kv OHTL was cut and fell on ground , the cable was still live although being protected by Earth fault relays and Over current relays(Instantaneous and Time delay) , but for some reason they failed to operate.

This incident caused death of over 30 camels in Saudi Arabia.

This line was located in the desert and the marks on the sand showed that it stayed on ground for longer than one day.

What do you think could possibly cause EFR and OCR not to operate?

All opinions are much appreciated.

Thank you in advance
 

Answers and Replies

  • #2
berkeman
Mentor
56,650
6,551
The Earth ground fault will only trigger if there is a good ground fault, so if the wires landed on dry sand or dirt, the GFCI may not trip. Also, if both wires fell together, then the current might have looked differential, and again the GFCI would not trip.
 
  • #3
dlgoff
Science Advisor
Gold Member
3,790
1,674
I agree with berkeman. High resistance of the soil(sand) could cause both relays to not sense the downed lines. The gound potential rise near the lines would cause the animals to be killed. With there long steps, there would be a large potential difference between the legs.
 
  • #4
Tee
8
0
Thanks for the replies , that was really helpful.
 
  • #5
Also:

Non directional ground relays may operate is the setting is below the current unbalance setting. Normally they set above to prevent inadvertent tripping during high demand period, typical in feeder circuits fro their neutral protection.

Tansmission system are trated as a balance circuit which can be set much lower in percentage terms to feeder circuit rating and often can be set to operate for broken conductor or single line to groundf ault with very low fault current on dry terrain or high ground impedance ... abnormal case for setting describe above.
 
  • #6
good analysis
but
what are the suggested solutions for this problem in desert ?
 

Related Threads for: Overhead transmission line protection failure

  • Last Post
Replies
2
Views
6K
Replies
4
Views
5K
Replies
15
Views
2K
Replies
21
Views
3K
Replies
20
Views
2K
  • Last Post
Replies
6
Views
6K
Replies
4
Views
783
Top