Power Factor Circuit Design for Taman Maju Jaya, Rawang

Click For Summary

Discussion Overview

The discussion revolves around designing a power factor correction circuit for a terrace house in Taman Maju Jaya, Rawang. Participants explore how to calculate the total power factor and methods to improve it to 0.98, considering the specific electrical loads present in the house. The context includes both theoretical calculations and practical considerations for implementation.

Discussion Character

  • Technical explanation
  • Homework-related
  • Exploratory

Main Points Raised

  • One participant outlines the problem scenario, detailing the electrical loads and their respective power factors, and seeks guidance on starting the calculations for power factor correction.
  • Another participant clarifies that the loads are in parallel and suggests calculating the apparent power for each load based on the given active power and power factor, noting that most loads are likely inductive.
  • There is a suggestion to add a parallel branch to eliminate reactive power once the total apparent power is determined.
  • One participant expresses a belief that the circuit design is straightforward, referring to it as an "easy parallel circuit."
  • A later reply emphasizes the importance of considering the operational status of the appliances, suggesting that power factor correction might need to be tailored to individual loads rather than the entire house.
  • Another participant provides additional context about wiring in North America, discussing the implications of balancing loads between phases and the complexity of power factor correction in different scenarios.

Areas of Agreement / Disagreement

Participants generally agree on the parallel nature of the circuit and the approach to calculating apparent power. However, there is uncertainty regarding the operational status of the appliances and whether to correct the power factor for the entire house or individual loads, indicating multiple competing views.

Contextual Notes

Participants have not specified assumptions regarding the operational conditions of the appliances, which may affect the power factor correction strategy. There is also a lack of consensus on whether to approach the problem from a whole-house perspective or focus on individual loads.

APEX25
Messages
3
Reaction score
0
PLEASE HELP ME, GOOD ENGINEER :D

Problem Scenario

As an electrical engineer in Rawang Power Electrical Consultant Company, your boss assigned your group to design a power factor circuit to improve the low power factor in one terrace house in Taman Maju Jaya, Rawang. The terrace house received a power supply 240V, 50Hz from TNB. The loads in that house consist of :



Device , Units ,Active Power ,Power factor
Florescent Lights ,10 ,40W each , 0.5
Air-conditioning ,4 ,750W each , 0.7
CFL Lights ,7 25W each , 0.6


Your group needs to produce the best proposal on designing a power factor circuit to improve the power factor to 0.98 and verify your design with appropriate simulation program.
Compare the current, power factor, apparent power, reactive power and active power consumed before and after the power factor correction exercise.
Write a brief proposal contains the design and findings.

the problem is where should i start first, how to calculate total power factor and correct it to 0.98?
 
Physics news on Phys.org
APEX25 said:
The terrace house received a power supply 240V, 50Hz from TNB.

Device , Units ,Active Power ,Power factor
Florescent Lights ,10 ,40W each , 0.5
Air-conditioning ,4 ,750W each , 0.7
CFL Lights ,7 25W each , 0.6

the problem is where should i start first, how to calculate total power factor and correct it to 0.98?

All those loads are in parallel. Each load is specified in watts (and active power is mentioned) so their power draw is real power. If it was apparent power it would be specified in VA. Most loads are inductive so unless it tells you or you know otherwise from the type of load, you should assume these loads are inductive.

So given the power factor and the fact these loads are inductive and appear in parallel, you can calculate the apparent power of each parallel branch.

Since each branch sees the same voltage, the apparent powers can be added to determine the total apparent power delivered to the house. This can be done because the current into the home is the sum of the currents in each branch.

Once you have the total apparent power demanded for the home, you can look at adding another parallel branch to eliminate the reactive power.
 
thanks... so that means it just a easy parallel circuit?
 
APEX25 said:
thanks... so that means it just a easy parallel circuit?

Yes, think of how a house is wired. Each appliance will get the full 240V (in your country!) so they are all wired in parallel.

I don't see anything about how often these appliances are on, etc, so I don't know if you need to worry about whether all loads are assumed on all the time for your power factor correction. In real life you would be worried about that so you may wind up doing power factor correction for individual loads instead of the entire home.In North America, it can get slightly more complicated. Homes are served by the secondary of a center tapped transformer so three wires come in -- a neutral from the center tap and two hot wires at 120V out of phase by 180 degrees. So you have each of those two phases running down alternate rows of the main box and the electrician wants to balance the load between the two phases. Then you also have the option of taking the voltage across the two phases to a load to have 240V service for certain high power appliances like driers and ovens.
 
Last edited:

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
Replies
8
Views
2K
  • · Replies 7 ·
Replies
7
Views
6K
  • · Replies 9 ·
Replies
9
Views
5K
  • · Replies 10 ·
Replies
10
Views
5K
  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 14 ·
Replies
14
Views
4K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 8 ·
Replies
8
Views
6K
  • · Replies 10 ·
Replies
10
Views
5K