Hello all. I recently read something that has me a bit confused. Consider a single-phase 100kVA transformer that supplies a 40kW heating load at unity power factor. What is meant by "how much additional kW of inductive load at 0.8 power factor can the transformer carry" mean? Is it asking how much more real power will the supply be transferring to the load given it is no longer unity?
Seems odd talking about a transformer "carrying" kiloWatts.
 
Engineering news on Phys.org
  • #2
40 kW at 1 PF is 40 kVA. 100-40 is 60. So how many kW is 60 kVA at .8 PF? Yes, that's real power.
 
  • #3
(60 kVA)0.8=48 W.
Essentially they are simply wanting to know how much more real power the source can supply to a load with 0.8 PF given it is still supplying the unity PF heating load?
 
  • #4
Thats the way I read it. It's asking how much additional load can be added to the transformer assuming all additional loads have a PF of 0.8.

So yeah, 48KW of true power will give you an apparent power of 60KVA at a PF of 0.8.
 
Last edited:
  • #5
Word problems are best parsed carefully.
Word problem authors don't always give the facts in a logical sequence.
I don't know if that's because English is such a mishmash of Olde English, Latin and Old Germanic, but English works well enough if one is careful about transcribing it into equations...

First impulse is to leap to the answer -there's 60 kva of room left at .8 pf so answer is 48.

That was my first answer but i think it's wrong. Too much internet has made me impatient.

Going back to ninth grade algebra and geometry,
We started with just a line - no imaginary component.
Adding some kva at an angle changed our line into a triangle that represents our real(kw) and imaginary(kvar) and total(kva) components.

specifically, a right triangle whose hypotenuse is 100 kva
and whose two sides represent real and imaginary power,, kilowatts and kilovars respectively.

so :
let x = real kw to be added.
PF of .8 defines a 3-4-5 right triangle,
so if x kw of real power are added,
then (3/4)x kvar of imaginary power are added
and (5/4)x of total kva are added ;

the resulting right triangle has
real side (40 + x) kw
imaginary side (3/4)x kvar
hypotenuse 100 kva

so pythagoras says
(40+x)^2 + (0.75 x)^2 = (100)^2

which by quadratic equation gave me
x = 52.06183 kw real
and (3/4)x = 39.0467 kvar imaginary
and a quick check by windows calculator:

sqrt( (40 + 52.0618)^2 + (39.0467)^2 ) = 100

so answer could be 52.0618 kw added instead of 48 ...
(and 65.0773 kva instead of 60) .

would somebody check my thinking and algebra?

And is phrase "kW inductive load" an oxymoron, or am i nitpicking?

old jim
 
Last edited:
  • #6
Yeah, this is exactly why I asked. I felt as though it was worded awkwardly; in a way that none of my textbooks have ever worded a problem. I see where you are coming from, though.
I drew a phasor diagram, ended up with two triangles, then applied Sine Law and ultimately ended up with the same result as you! Regards!
 
  • #7
Thanks Sandy - diverse methods came to same number, so i am convinced it's right.

But what a wakeup it was for me to see how easily i leapt to wrong answer !

my self discipline needed a tuneup..

I wonder if that was a subtle choice of words, or did author make same mistake?

thanks

old jim
 

FAQ: Power Factor & Transformer Load: 40kW to 100kVA

1. What is the difference between power factor and transformer load?

Power factor refers to the ratio of real power to apparent power in an electrical system. It measures how efficiently the electricity is being used. Transformer load, on the other hand, refers to the amount of power that a transformer can handle. It is usually expressed in units of kilovolt-amperes (kVA) and represents the maximum amount of power that can be transmitted through the transformer.

2. How does power factor affect transformer load?

A low power factor can increase the transformer load, as it requires more current to deliver the same amount of power. This can cause the transformer to overheat and potentially fail. On the other hand, a high power factor reduces the transformer load, as it allows for more efficient use of the electricity. Overall, maintaining a high power factor is important for the proper functioning and longevity of transformers.

3. Can the power factor of a transformer be improved?

Yes, the power factor of a transformer can be improved by installing power factor correction equipment, such as capacitors, in the electrical system. These devices help to reduce the reactive power, which in turn increases the power factor. It is important to regularly monitor and maintain the power factor to ensure optimal performance of the transformer.

4. What is the significance of the 40kW to 100kVA ratio in transformer load?

The ratio between kW (real power) and kVA (apparent power) is a measure of the power factor. In this case, the ratio is 0.4, which indicates a low power factor. This means that for every 100kVA of power being delivered, only 40kW is being used efficiently. This low power factor can increase the transformer load and affect the overall performance of the transformer.

5. How can the transformer load be calculated?

The transformer load can be calculated by dividing the total power consumed by the system (in kW) by the power factor. For example, if a system is consuming 80kW of power with a power factor of 0.8, the transformer load would be calculated as 80kW / 0.8 = 100kVA. It is important to note that the power factor can vary and should be monitored regularly to accurately calculate the transformer load.