Hi all, a pretty simple question. I want to be able to calculate the load on a 100amp 3 phase service. As an example if I have 9 lighting fixtures that are rated @ 11 amps 208v each (auto ranging 200-240v actually but service will be 3 phase so 208v ish)
Putting evenly across each leg x,y,z I get 66 amps per leg. At this point you would multiply by 1.732 or divide by 1.732 each leg total to get a more accurate load? Or am I missing a step? Or just totally off...
What is the purpose of the sqrt of 3?
Where does power factor come in? How is power factor determined?
Also, if you metered a 208v system that let's say has 8 units instead of 9, would that voltage difference be seen on the neutral and nothing on the ground? The neutral should be able to carry up to the rating of the cable rating? A service from the power company can handle unbalanced loads as opposed to a smaller generator which one would want to balance with more care?
Thanks for your expertise.
Putting evenly across each leg x,y,z I get 66 amps per leg. At this point you would multiply by 1.732 or divide by 1.732 each leg total to get a more accurate load? Or am I missing a step? Or just totally off...
What is the purpose of the sqrt of 3?
Where does power factor come in? How is power factor determined?
Also, if you metered a 208v system that let's say has 8 units instead of 9, would that voltage difference be seen on the neutral and nothing on the ground? The neutral should be able to carry up to the rating of the cable rating? A service from the power company can handle unbalanced loads as opposed to a smaller generator which one would want to balance with more care?