Pressure loss to double wall pipe (ventilation)
13 replies · 4K views · last reply
longz
Hi every body,
I need help to calculate the pressure drop to double wall pipe with information as below, i understand need calculate pressure loss to the straight pipe, elbows and supports but I don't know exactly how.
- Fluid : air
- Double wall pipe (stainless steel) with outer pipe OD89mm, wall thickness 3mm, inner pipe OD61mm, wall thickness 2mm. the air will blow into the void between inner and outer pipe
- Pipe distance : 7m.
- Number of 90 degree elbow : 7 pcs
- Number of plastic support to inner pipe : 9 pcs
- Air flow capacity 28 m3/h equivalent 7.8 L/s.
Some drawing for clear view:
1. Double wall pipe section
2. Double wall pipe section with support, the support is obstruction to the air flow similar to orifice.
3. Elbow
Thank every body.
Hi Chestermiller,
I need to determine the pressure drop to the air.
Thank
longz said:
Hi Chestermiller,
Thank
If the air were flowing through a circular pipe, would you know how to get its pressure drop? If so, please describe.
I have no idea, can you provide some instructions ?
thank
thank
See chapter 7 of Transport Phenomena by Bird, Stewart, and Lightfoot.
I really sorry as I can't get this book, can you advise the specific mathematic formula ?
Hi Chestermiller,
I made a study and draft a calculation to pressure drop but I not sure it is correct 100% or not, can you please have a check and correct me if i was wrong something.
thank
longz said:
Hi Chestermiller,
thank
I didn't check your arithmetic, but I can tell you that you have done this exactly the way I would have done it. Very nice work. Kudos!
Chet
Hi Chestermiller,
I found a online calculator exactly same to this matter but the result is quite different in Reynold number (509853 versus with 4988 as mine calc.) caused me confusing, can you please have a look and advise the reason? below is the link of software and information input/output.
http://www.pressure-drop.com/Online-Calculator/index.html
Input calculation
Output calculation
longz said:
Hi Chestermiller,
Input calculation
Output calculation
In their calculation output, the viscosity used looks too low by a factor of 100.
Hi Chestermiller,
Thank for advices, you are correct. I changed the value of the viscosity and the software output similar to mine calc.
To pressure drop of inner pipe support ring, could you please advise some instructions ? I considering this is multi-hole orifices plate but the point is the holes is not same and have multi plates on the pipe route. I don't know how to start the calculation.
longz said:
Hi Chestermiller,
In a case like this, you have to use your best judgment as to whether the multi-hole is adequate. Compared to the total pressure drop, how much does the pressure drop across the plate matter?
Simple CFD analysis using the default laminar flow model in OpenFoam .
5 m/sec uniform air velocity at inlet . Zero pressure (gauge) at outlet . Air flows from left to right .
So roughly 110 Pa pressure drop per support plate . Almost nothing really and certainly negligible .