Hi every body,
I need help to calculate the pressure drop to double wall pipe with information as below, i understand need calculate pressure loss to the straight pipe, elbows and supports but I don't know exactly how.
- Fluid : air
- Double wall pipe (stainless steel) with outer pipe OD89mm, wall thickness 3mm, inner pipe OD61mm, wall thickness 2mm. the air will blow into the void between inner and outer pipe
- Pipe distance : 7m.
- Number of 90 degree elbow : 7 pcs
- Number of plastic support to inner pipe : 9 pcs
- Air flow capacity 28 m3/h equivalent 7.8 L/s.
Some drawing for clear view:
1. Double wall pipe section
2. Double wall pipe section with support, the support is obstruction to the air flow similar to orifice.
3. Elbow
Thank every body.
Which are you trying to determine, the pressure of the water or the pressure of the air?
Hi Chestermiller,
I need to determine the pressure drop to the air.
Thank
longz said:
Hi Chestermiller,
Thank
If the air were flowing through a circular pipe, would you know how to get its pressure drop? If so, please describe.
I have no idea, can you provide some instructions ?
thank
thank
See chapter 7 of Transport Phenomena by Bird, Stewart, and Lightfoot.
I really sorry as I can't get this book, can you advise the specific mathematic formula ?
Hi Chestermiller,
I made a study and draft a calculation to pressure drop but I not sure it is correct 100% or not, can you please have a check and correct me if i was wrong something.
thank
longz said:
Hi Chestermiller,
thank
I didn't check your arithmetic, but I can tell you that you have done this exactly the way I would have done it. Very nice work. Kudos!
Chet
Hi Chestermiller,
I found a online calculator exactly same to this matter but the result is quite different in Reynold number (509853 versus with 4988 as mine calc.) caused me confusing, can you please have a look and advise the reason? below is the link of software and information input/output.
http://www.pressure-drop.com/Online-Calculator/index.html
Input calculation
Output calculation
longz said:
Hi Chestermiller,
Input calculation
Output calculation
In their calculation output, the viscosity used looks too low by a factor of 100.
Hi Chestermiller,
Thank for advices, you are correct. I changed the value of the viscosity and the software output similar to mine calc.
To pressure drop of inner pipe support ring, could you please advise some instructions ? I considering this is multi-hole orifices plate but the point is the holes is not same and have multi plates on the pipe route. I don't know how to start the calculation.
longz said:
Hi Chestermiller,
In a case like this, you have to use your best judgment as to whether the multi-hole is adequate. Compared to the total pressure drop, how much does the pressure drop across the plate matter?
Simple CFD analysis using the default laminar flow model in OpenFoam .
5 m/sec uniform air velocity at inlet . Zero pressure (gauge) at outlet . Air flows from left to right .
So roughly 110 Pa pressure drop per support plate . Almost nothing really and certainly negligible .