Pumping power calculation of a vertical closed-loop system

In summary, the pumping power required for fluid circulation depends only on the fluid flow and the pressure differential between the inlet and outlet of the pump.
  • #1
argeus
2
0
TL;DR Summary
pumping power calculation of a vertical closed-loop system assuming the hydrostatic term
Hi there,
I hope that somebody can help me with this.. Any response is much appreciated!

Let's have a vertical closed-loop system where the fluid circulates using the pump. The temperature in both sections gradually changes (the upcomer section is heated up) so that the densities, velocities, and pressure drop change as well. Hence, it would be beneficial to split the geometry into horizontal sections; each section (downcomer and upcomer) is divided into a certain number of elements, each of the same height. The point is to calculate the pumping power needed for fluid circulation. The total power is calculated per partes, i.e. for each ith row separately and then simply summed together.

1677502151535.png


For any single ith row, the pumping power equation (w/o hydrostatic term) yields:
1677502566704.png

Note that subscript a refers to a downcomer and subscript b to an upcomer, respectively. Symbol m refers to the mass flow rate, ρ is density and Δp is the pressure drop across the element in the ith row as per Darcy friction eq.
Now assuming a hydrostatic pressure due to the changing density, one gets:
1677502594418.png

Simply, g denotes gravitational acceleration, and the term dl refers to the height of the element in the ith row.
Rearranging a bit:
?hash=1292ae7e36b7eaa26def673fa23d82f0.png

Since the mass flow is the same in both channels, we finally get:
1677502657295.png

Does this mean that the pumping power is independent of the hydrostatic pressure in the closed loop even when the fluid densities in both vertical channels differ? This does not seems correct to me, however, simply cannot find where I'm going wrong..
 

Attachments

  • 1677502617665.png
    1677502617665.png
    1.6 KB · Views: 65
Last edited:
Engineering news on Phys.org
  • #2
Welcome @argeus !
Pumping required power depends only on fluid flow and pressure differential between inlet and outlet of the pump.
 
  • #3
argeus said:
Does this mean that the pumping power is independent of the hydrostatic pressure in the closed loop even when the fluid densities in both vertical channels differ?
Rewriting your equation:
$$P = \rho_a \dot{V}_a\frac{\Delta P_a}{\rho_a} + \rho_b \dot{V}_b\frac{\Delta P_b}{\rho_b}$$
Where ##\rho_a \dot{V}_a = \rho_b \dot{V}_b =\dot{m}##. Simplifying:
$$P = \dot{V}_a\Delta P_a + \dot{V}_b\Delta P_b$$
 
  • #4
Dear Lnewqban,

Thank you for your reply. This is completely true and it matches the first eq. However, the question of how the pressure differential should be calculated remains open. I would guess that it consists of two terms, i.e. frictional forces and hydrostatic forces. If the temperature in the upcomer section is higher (because this section is heated), the density decreases and the hydrostatic balance should promote fluid flow. This is how thermosiphons (aka heat pipes) work. In a specific case, the hydrostatic force difference could balance the frictional forces so that a natural circulation in the closed-loop system is established and no pump is needed. For instance, the geometrical integrity of the Trans-Alaska Pipeline System in a permafrost environment is maintained using such heat pipes. So neglecting the hydrostatic term indicates to me that I've just overlooked something..
 
  • #5
That difference of temperatures, if substantial and continuous due to good heat transfer on both halves of the loop, may help your pump.
If most thermal energy does not remain in the fluid, something else is needed to stablish and keep a flow, overcoming friction and turbulence.
There is phase change in a heat pipe, you don’t have that in your system.

Nevertheless, at start up, that T differential may not be there, and your pump will need to have increased power to overcome friction of the system at an intermediate temperature.

If you have valves, expansion tanks, aireators, thermometers, coils, etc. in your loop, you will need to calculate pump power for worst conditions (full flow and restricted flow with all closed valves, restricted coils, air pockets traped in horizontal pipes, etc.).
Therefore, a safety factor should be included in your calculations as well.
 

1. What is pumping power calculation and why is it important for a vertical closed-loop system?

Pumping power calculation is the process of determining the amount of power required to move a fluid through a system. It is important for vertical closed-loop systems because it helps to ensure that the system is operating efficiently and can help identify any potential issues or inefficiencies.

2. How is pumping power calculated for a vertical closed-loop system?

The pumping power for a vertical closed-loop system can be calculated using the following formula:
P = (Q x H x ρ x g) / η
Where P is the pumping power in watts, Q is the flow rate in cubic meters per second, H is the total head in meters, ρ is the density of the fluid in kilograms per cubic meter, g is the acceleration due to gravity in meters per second squared, and η is the pump efficiency.

3. What factors can affect the pumping power calculation for a vertical closed-loop system?

There are several factors that can affect the pumping power calculation for a vertical closed-loop system, including the flow rate, head, density of the fluid, pump efficiency, and the type of pump being used. Other factors such as pipe diameter, friction losses, and elevation changes may also impact the calculation.

4. Can pumping power be reduced in a vertical closed-loop system?

Yes, pumping power can be reduced in a vertical closed-loop system by optimizing the design and operation of the system. This can include using a more efficient pump, reducing flow rates, minimizing head losses, and ensuring proper maintenance of the system.

5. How often should pumping power calculations be performed for a vertical closed-loop system?

Pumping power calculations should be performed regularly, especially when there are any changes or modifications made to the system. It is recommended to perform these calculations at least once a year to ensure the system is operating efficiently and identify any potential issues that may arise.

Similar threads

  • Mechanical Engineering
Replies
6
Views
2K
Replies
3
Views
2K
  • Mechanical Engineering
Replies
9
Views
3K
  • Mechanical Engineering
Replies
8
Views
778
  • Materials and Chemical Engineering
Replies
16
Views
436
Replies
26
Views
4K
Replies
2
Views
1K
  • Mechanical Engineering
Replies
1
Views
1K
Replies
40
Views
4K
  • Mechanical Engineering
Replies
13
Views
2K
Back
Top