  1. Nov 10, 2016 #1
    In a transformer, let's say we have:
    I1, I2 - currents through the primary and secondary winding
    V1, V2 - voltages
    N1, N2 - number of turns
    F1, F2 - magnetic fluxes through core, produced by the currents I1 and I2 (they are opposing...)
    R - the reluctance of the core

    We have V1/V2 = N1/N2 = I2/I1.
    F1=N1*I1/R; F2=N2*I2/R
    I think I1 and I2 are in phase too.
    That means F1 and F2 are practically equal.
    How can we have a nonzero resulting flux through the core? F=F1-F2
    If the flux through the iron core is zero, then the cause that produces V2 (variation of the flux) does not exist, then V2=0?
    I know I'm wrong, but i don't know where is the mistake...
     
  2. jcsd
  3. Nov 10, 2016 #2

    BvU

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Hello helene, :welcome:

    As you say, the driving force for induction emf is not the flux itself, but the change in the flux. To keep up counteracting F1 with F2, the amplitude of V2 has to be nonzero.
     
  4. Nov 10, 2016 #3

    Hesch

    User Avatar
    Gold Member

    Say that the impedance in the primary coil = Z1. Then the transformer will balance the flux through N1 so that

    ( Vsupply - dψv/dt ) / Z1 = I1 as for the primary coil when the transformer is unloaded. ( ψv = Flux * N1 ).

    I1 is the current needed for magnetizing the core so that this balance is achieved.

    Say that I1 is too small, ψv will be too small → the back emf will be too small → the voltage difference ( the parentheses above ) will be to high, so that I1 will increase.

    If you load the transformer, I2 will decrease the flux so that I1 must increase to keep up balance.
     
  5. Nov 11, 2016 #4

    jim hardy

    User Avatar
    Science Advisor
    Gold Member
    2016 Award

    realize that I1/I2 isn't exactly equal to turns ratio.
    There is small magnetizing current to produce flux enough to oppose applied voltage. It flows in primary winding only and is a loss.
    But in a power transformer it's quite small compared to load current so is generally ignored. In the golden era of slide rule accuracy(3 digits) it was a quite reasonable approximation.

    Have you studied equivalent circuit of a transformer ?
    https://en.wikipedia.org/wiki/Transformer

    Do you have a lab at school where you could apply variable voltage to a transformer and plot magnetizing current ?

    old jim
     