A 5 to 20 bar reverse acting proportional pressure controller has an output of 4 to 20 mA. The set point is 11 bar. Determine:
(a) the measured value pressure which gives an output of 15 mA when the proportional band setting of the controller is 40%
(b) the proportional band setting which will give an output of 8 mA when the measured value is 14 bar and the desired value is 11 bar.
Can anyone help me with my findings whether i am in the right direction?
Part (b) should be a figure or a %? Thanks
(a)
PB = 40% = 0.4
Controller output (Co) = initial control valve + (error x gain)
Gain Comax - Comin / PB = -(20-4) / 0.4= - 40
error e(t) = SP - MP
Controller output = Comax + Gain (SP - MP) 15 = 20 - 40 (11 - MP) MP = 10.9 bar(b)
Controller output = Comax + Gain (SP - MP) 8 = 20 + Gain (11 - 14) Gain = 4
4 = 16 / PB = 4
Hi, have you resolved your problem yet?
I'm struggling with this.
So far I've got 4ma = 5 bar and 20ma=20bar... So, 15ma is equal to 4ma +11ma which is an increase of 68.75%. 68.75% of 5-20bar is 10.3125bar.
So, a 15mA signal will give 10.3125 bar if the PB were 100%? I'm not sure how to work in the PB of the controller being 40%
Does 4mA = 20 bar and 20mA = 5bar ?? (Reverse acting)
Yes.
Thanks for that, I am trying to work this out based on examples given in lessons but they are not clear.
Can you look at the attachment. This contains 2 examples from the lesson I am following.
There are 2 diagrams each with 3 proportional bands, 30%, 50% and 100%. They are all centered at 50% of the measured value.
I understand from this that the proportional band is always associated with the measured value, the input which in the case of this question, is the pressure, 5 - 20 bar. This will be the x axis
The controller output is 4 - 20 mA. This is the y axis
So for this question I think that I could create a graph similar to the attached examples with the 5 - 20 bar input on the x-axis and the 4 - 20 mA as the Y axis.
The scaling of the pressure would have to be reduced (squeezed) to 40% on the x axis, centered around 50% of the measured value.
From this I should be able to strike a line from the 15 mA mark on the y-axis and find the approx pressure required to generate a value 15 mA from the x axis
Does this make sense ??
Or should the PB be centered around the set-point or desired value, which in the case of this question, is 11 bar
I think it will be easier to see if you start by drawing a graph similar to the first one in your attachment, but with the axes labelled with the actual pressure and the actual current output of the controller. Start both axes at Zero and initially draw the graphed line for the full working range of the pressure with the controller covering 100% of the pressure range.
Hello again, I worked on this yesterday, trying different methods and I have attached my examples. I seem to get a value of approx 9.75 bar in all cases no matter where I position the PB. I am not sure if this is the correct approach or not and I am not able to mathematically verify this value of 9.75 bar. I am not sure how to do that.
In the first instance could you look at my graphs and advise if this is the correct approach or not please. My "first attempt" is in answer to your advice in the last post
Hmmm. Your results work ONLY IF YOU CAN CHANGE THE OFFSET to get the (a) and (b) answers.
Given the problem statement, I would design on the basis of 20 bar pressure always gives 4mA output, and then, if possible, to use one PB that could cover both parts (a) and (b). If more than one PB is needed for the two questions, then state/show the two different values.
Does the original problem, or its context, say anything about offsets? The problem statement given in this thread refers only to the "proportional band setting" with no mention of even the concept of "offset."
It would be a big help if someone can copy and paste the original problem.
Optional:
If you want to generate a formula for a final answer rather than a graph, I suggest that the graph 'Y' axis start at Zero current. This will make it more obvious when generating the formula that there is an offset. (it's easy to forget otherwise :biggrin:)
Cheers,
Tom
p.s. This has got me thinking some too; it has been a few decades since I've used these!
Hi
The original problem is copied below. It does not mention offsets so I have to assume tat the control loop is stable and the controller is set up properly. The 3 graphs I posted were my attempts, varying the position of the PB with respect to the measured value. I am wondering if I am looking to deeply into this because part B of the question seems to be written in a way that can be calculated if I knew of the equation
A 5 to 20 bar reverse acting proportional pressure controller has an output of 4 – 20 mA. The set point is 11 bar. Determine:
(a) The measured value pressure which gives an output of 15 mA when the proportional band setting of the controller is 40%
(b) The proportional band setting which will give an output of 8 mA when the measured value is 14 bar and the desired value is 11 bar
In the first post of this thread there is an equation (see below) which I think assumes there is an error but the result of that calculation (10.9) does not agree with my graphs so that has kind of thrown me of the route a bit
PB = 40% = 0.4
Perhaps we are interpreting the problem statement differently.
I am reading that as there being a self-contained pressure controller that reports the measured outlet pressure to the 4-20mA loop.
Another interpretation could be a proportional pressure valve that is driven by a controller... which seems to be the interpretation you are using.
The apparent ambiguity of the problem statement in the First Post is why I asked for the ORIGINAL statement, as in a link to where it appeared or at least a copy-and-paste.
I have put in a request for other any other Advisor to join this discussion to help sort things out.
Cheers,
Tom
Ok thanks for the update, hopefully we can solve this
I was given a small amount of information regarding this, an example which could help.
As we have said the
"controller is reverse acting hence 20mA corresponds to 8 bar and 4mA to 14 bar. 6 bar pressure change = 16mA then calculate for output of 15mA (i.e a change of 11mA from 4 to 15)"
I can't work out how the above statement can be incorporated in this problem but it obviously can be
It may help to realize that a straight-line graph can be characterized by its Slope-Intercept form, Y=mX+b. You made use of that in your earlier calculations.
Y= Dependent variable
m= Slope of the line
X= Independent variable
b= Y Intercept
Cheers,
Tom
I have been unofficially told that one of my earlier graphs was actually correct although there are other methods of calculating this question. What I am trying to do now is mathematically work out the answer. I know the answer is approx. 9.75 bar for a 15mA signal when the PB is 40%. I am just trying to prove the math now. I need to read up on Y=mX+b as I think there maybe some differential in there which is not my strong point
I would venture that
as @Tom.G suggested
y = mx + b is the right approach.
I'd make y be output milliamps
and x be input bars.
so as to make the independent variable, pressure, plot on the X axis
and the dependent one , milliamps, on the y axis.
x and m and b are not simple single term constants though.
Look at the units - we have to get from psi to ma,
so m will be the product of at least two individual m's -
one for units conversion let's call it munits
and another for controller gain which is 1/(proportional band) let's call it mgain
and m's sign will reflect direct or reverse acting..
Next, since controllers operate on an error signal, namely difference between input and setpoint,
input x will be that difference namely (pressure - setpoint)
so x = (bars - setpoint)
lastly b will take care of the 4ma offset in controller output.
But there's a sneaky little fact not mentioned in the problem statement, namely,
... in the absence of directions to the contrary you set up controllers so they have 50% output at zero error
that way they'll control somewhere around mid output and not bang against a limit.
so our b term also takes care of the fact that at zero error, ie x = zero,. the controller's output will be 50% or 12 ma.
meaning b is 12 ma not the 4 you'd likely think. .
y = munits X mgain X (input - setpoint) + 12 milliamps
so let's step through what we know
He didn't state at what proportional band that relation holds so let us assume it's at pb of 100%, meaning it take a fullscale change at input to cause a fullscale change at output.
So, munits = Δoutput / Δinput = 16 ma / 15 bar
Furthermore, since it's reverse acting, ie increasing input causes decreasing output,
Δ's in numerator and denominator have opposite signs
meaning munits must be negative.
So munits = -(16/15) ma / bar .
aha ! Error then will be (pressure -11) bars and that's x .
x = (bars - 11)
Great ! He's told us pb is 0.4 which is 1/(controller gain),
That makes mgain =2.5 ,
and m = munits X mgain = -16/15 X 2.5 = = -8/3
and x = pressure - 11
Now y = mx + b
and y = 15
so
15 = -8/3 X (bars-11) + 12
(15-12) X 3/8 = -(bars - 11)
9/8 = 11 - bars
bars = 11 - 9/8 = 9.875
okay,
y = 8
x is (bars - setpoint) = (14-11) = 3
b is 12 as before
solving y = mx + b for m
8 = m X 3 + 12
(8 -12 ) / 3 = m = -4/3
since m = munits X mgain
mgain = m / munits = ( -4/3 ) / (-16/15) = 5/4 ,
so pb = 1/mgain = 1/(5/4)= 0.8 = 80%
[ it's latei= --- i hope i didnt bungle my arithmetic. ]Does above make sense ?
There's no step that is complicated. Just you have to be meticulous.
let me know if you find a mistake.
old jim
Wow those would be two different problems with different answers.
Old adage "A question well stated is half answered... "
I sure missed that ambiguity. (red faced chagrin icon)
Seems to me that were this gizmo reporting measured process pressure its setpoint and PB would be superfluous .
it would be acting as a simple pressure transmitter with simple span and zero adjustments.
Asking about PB and Setpoint would be a misleading "dirty trick" on students.
old jim
Gents
Post 18 is correct. It makes a lot of sense to me now. In past lessons I have seen the use of y = mx + b but never connected it with this problem. I had confirmation that my graph was correct and your answer in post 18 mathematically proves that. All I need to do now is revisit the lessons using this and understand how it calculates in this case. I don't think I am finished with this just yet but very close now. Thanks to you both (Tom and Jim) for helping out with this so far
Good Morning, just a recap, last night I followed up on the advice given in posts 16 and 18. I found a website (link below) that focuses on this area
http://www.math.com/school/subject2/lessons/S2U4L2GL.html
Just one final question.
Do you mean that unless there is an error stated we always assume that x = zero? In the case of this question there is an error (x = (bars - 11) What kind of example would show an error? How would we know if there was an error in the question? I understand `b` but if you had not explained this I would never have assumed b = 12 mA and not 4 mA
I have attached the graph I keep talking about and marked on it the exact center of the output which equals 12 mA
i am not sure i understand your question "What kind of example would show an error?"
To me, the term "controller" defines that we're dealing with some sort of automatic control system.
The basic idea behind Automatic Control is to measure something and take some physical action action to hold it at or near a desired value.
Call that something "the process" , it might be a temperature, a flow, a pressure, or anything else in our modern world.
To accomplish that we measure the process and compare its value to a desired value.
In my day we just called measured value "process" and desired value "setpoint".
Error is always the difference between those two..
There are lots of turorials out there just search 'basic automatic control'
my first hit was http://www.ent.mrt.ac.lk/~rohan/teaching/EN5001/Reading/DORFCH1.pdf
try a few and find one that suits your taste
in this one your reverse acting controller includes the error summer (circle) and control device that i highlighted in red ..
Actuator will be something that moves according to the controller's 4-20 milliamp output.
In my plant we controlled pressure with 400 kilowatts of electric heaters that boiled water into steam to maintain pressure at 2235 psi.
The 4 to 20 ma signal controlled heater power over a narrow range of pressure , i forget the exact value perhaps 50psi.
That would mean Setpoint of 2235 , at 2210 heaters would be full on (400 kw) and at 2260 fully off and at 2235 50% 200 kw.
That's oversimplifyimg a little because our proportional controller had a second function called "integral"
but should convey the idea.
not at all, read on.
Error is always process minus setpoint ,or if your author prefers setpoint minus error, but always the difference.
Sometimes setpoint is calculated externally and applied as a second input to the controller.
You always arrange something downstream of the controller that enables it to drive process toward setpoint *hence error toward zero)
just like the feedback in an operational amplifier circuit.
If it's an automatic control system there's a process and there's a setpoint and their difference is error and in the problem you presented that's x.any help ?
old jim
those attached files ask to install on my computer and i don't want them on my disk, i just want to view in the webpage.
so i didnt look at them.
Does adobe offer you an option to make them not self-install ?
i just won't have self installing unknowns writing on my disk.
old jim
Hello Jim
The attachments are just graph paper. They are taken from a www.mathsphere.co.uk.
I use the graph paper online as I can get a more detailed result using the adobe system, apologies, I didn't know they try to self install.
I am more or less finished with this question now. Your help has been really appreciated.
I have snipped my graph below, not sure if you will be able to see it or not. You may need to enlarge it to see the detail. I didn't actually start this post so I can't mark it as solved but thanks for your help with this. I will no doubt come up against other problems like this as I am only half way through my control and automation module
https://www.physicsforums.com/attachments/234006
Thanks for the feedback.
I see our snip and paste although it is a little blurry wnen i enlarge it to 300%.
You might try the UPLOAD button
But i think you're flying now on your pwn wings, so - soar my friend !
Usually one just needs a small boost to get started up the learning curve.
Automatic control theory used to be called "cybernetics"
the concepts apply to everyday life too, not just hard science
there's an interesting old pop-psychology book by one Maxwell Maltz called "PsychoCybernetics"
i enjoyed it fifty years ago
should you spot it in a used bookstore for cheap, pick it up ,. You might enjoy it too and i'd be curious to know if it has cross generational appeal...
old jim
will certainly keep an eye out for that yes, thanks again
Hello again, I completed the calculation for 1b which was a PB of 80% as shown in post 18.
I have attempted to plot this on a graph in the same way I plotted for question 1a but I can't seem to get it to make sense. I have taken a line from 8 mA on the Y axis. This works out at approx 16.2 bar on the x-axis but it should be 14 bar. Below is a snapshot of the graph
Have I aligned the PB up correctly with the x-axis or should the set point of 11 bar be inline with the 40% mark or, should the set point (desired value) be in line with the 50% measured value
Below is snap shot of the attachment, I thought I was right with this but I am missing something in the plotting or scaling of this graph I think
  • Question 1b graph.pdf
remember
and (b) the proportional band setting which will give an output of 8 mA when the measured value is 14 bar and the desired value is 11 bar.
you need to shift your output current line until 50% output (12 ma) intersects a vertical line going straight up from setpoint, 11 bar,
3 bar from setpoint is 3/15 = 20% of input span away from setpoint,
which multiplied by 1.25 = 25% of output span = 4 milliamps away from balance point of 12 ma
and that'll cross at 8 ma
i think the y = mx + b equation holds true,
practice the longhand arithmetic method until you trust it
and then it'll be obvious to the eye when your computer graphing program is fooling you..
old jim
just for reference so i didnt have to flip pages
jim hardy said:
okay,
y = 8
b is 12 as before
8 = m X 3 + 12
So from the 12mA mark on the Y axis I need to take a horizontal line till it meets the vertical line from the 11 bar mark on the PB scale??
Where you have stated 3 bar from the set point is ##\frac{3}{15}=20##% then multiply this by 1.5 to get 25%. Should this not be 30% ? What is the 1.5 ??
David J said:
Where you have stated 3 bar from the set point is 315=20315=20\frac{3}{15}=20% then multiply this by 1.5 to get 25%. Should this not be 30% ? What is the 1.5 ??
Where do you see 1.5 ?
David J said:
1.25 is 1/PB and PB is 0.8
you need to move your output line left until it fits y=mx + b
milliamps = munits X mgain X (input - setpoint) + 12 milliamps
munits = -(16/15)
mgain = 1/PB = 1,25
m= munits X mgain = -(16/15) X 1.25 = -4/3
and B is 12 ma
so
ma = -(4/3) X (bars - 11) + 12
at 5 bars that's ma = -4/3 X (5-11) +12 = 20 ma
at 11 bars it's 12 ma
and at 17 bars it's 4 ma
if the controller is capable , at 20 bars it'd deliver zero ma.
this isn't right either
measured value is bars, 5 and 20 should align with 0 and 100 % .
So my line isn't quite right either
Fix that and replot your y = mx + b, see if it looks better.
this is how we learn don't get dejected
attention to detail is the key.
old jim
I think I am confusing myself with just where the PB needs to be positioned on the graph. I am placing the PB on the x-axis and associating it with the input which is bars.
I think the PB should be relating to the output which is mA in this question.
I have not been aligning 5 - 20 bar with 0 - 100% measured value, I have been shrinking it as a percentage of the MV which is why the graph is not making any sense
A snap shot from my notes below shows how the "output" is squeezed as a percentage of the measured value. In this case that is the mA output.
I will work on what you have said and see if I can grasp this
Thanks once again