Should the power supply float or be grounded?

Click For Summary
SUMMARY

The discussion centers on the grounding of power supplies, specifically whether to use a floating or grounded configuration. Participants highlight the importance of preventing insulation breakdown between transformer windings and the necessity of grounding for safety and compliance with NEC 2020 regulations. Grounding is essential when dealing with systems exceeding 150 volts to ground, particularly in commercial applications like induction heaters. The consensus leans towards grounding the secondary to ensure safety and mitigate electromagnetic interference (EMI) issues.

PREREQUISITES
  • Understanding of NEC 2020 regulations regarding grounding
  • Knowledge of transformer operation and insulation requirements
  • Familiarity with electromagnetic interference (EMI) concepts
  • Experience with power supply design, particularly for commercial applications
NEXT STEPS
  • Research NEC 2020 regulations on grounding for power supplies
  • Learn about transformer insulation techniques and safety standards
  • Explore methods to mitigate EMI in power supply designs
  • Investigate the implications of floating versus grounded power supplies in commercial devices
USEFUL FOR

Electrical engineers, power supply designers, safety compliance professionals, and anyone involved in the design and implementation of commercial electrical devices.

imsmooth
Messages
154
Reaction score
13
I have read pros and cons for both, but would like to hear what people have to say. I can build a simple power supply for a project that supplies 15v that is isolated from earth ground by using the output from a step-down transformer. I can also put one together that shares earth ground.

Which do people use for home projects and which do people use if its supplies power to some device used commercially or out in the field.
 
Engineering news on Phys.org
You need to prevent insulation breakdown, between the primary and secondary windings of the transformer. That suggests a common ground.

If a common ground is a problem, use a metal-oxide varistor, or a gas discharge suppressor, between the two ground systems. That will protect the transformer and you from static discharge.
 
  • Like
Likes   Reactions: DaveE
Circuits are normally grounded somehow, somewhere. As @Baluncore said, avoiding HV from leakage currents is one common reason. But multiple grounds can be a problem, if they aren't actually at the same potential. This is one reason people like isolated PSs. Then they can choose their own ground configuration.

In practice it can get complicated and depends on your performance requirements and the environment. Often things will work anyway, even if it's not perfect. To really answer this we would need much more information.
 
I agree with Baluncore.
In U.S.A the law it is NEC
NEC 2020
250.20 Alternating-Current Systems to Be Grounded
(A) Alternating-Current Systems of Less Than 50 Volts.
Alternating-current systems of less than 50 volts shall be grounded
under any of the following conditions:
(1) Where supplied by transformers, if the transformer
supply system exceeds 150 volts to ground
supply system is ungrounded
(2) Where supplied by transformers, if the transformer
supply system is ungrounded
(3) Where installed outside as overhead conductors
 
BS 7671 is more complicate .See for instance BS7671/2008

1684076233790.png
 
Thanks for the answers so far. My question about power supplies was just a general question, but here is a more specific one.

Let's suppose I was going to produce a commercial induction heater. (I'm not if anyone really wants to know). In it the coil and tank capacitor are not grounded - they are floating. The tank is coupled by a transformer to the inverter system.

The casing of the unit would be grounded. Would I have to have an earth ground to the LC tank? If I did then someone would complete the circuit by touching the work coil and make a path to ground. If it's isolated then there is no chance for shock unless the person grabs two ends with both hands, which would be strange thing for someone to do.
 
imsmooth10 said:
The casing of the unit would be grounded. Would I have to have an earth ground to the LC tank? If I did then someone would complete the circuit by touching the work coil and make a path to ground. If it's isolated then there is no chance for shock unless the person grabs two ends with both hands, which would be strange thing for someone to do.
To comply with the rules, and to be safe, you must ground the secondary somehow.
You must protect the transformer insulation from static leakage or short circuits.
 
There are ways to meet the safety standards with a floating secondary. This would be similar to an AC powered "double insulated" drill with a two prong plug, or your isolated power supply, for example. But, it's a pain in the #$$ and costs money. It probably wouldn't actually be done compared to grounding it. I won't go into all of the methods/requirements here, there are a few different implementation choices. Ask if you want more info/ references.
 
If the supply voltage of the transformer - before inverter- it is more than 150 V with respect to the ground, or if the transformer secondary is not grounded, you have to ground the tank. However, I agree with Baluncore , in any case, it is better to ground the tank.
 
  • #10
The choice of power supply floating or grounded depends entirely on the design specs, which includes requirements for safety and EMI (ingress and egress)

PC's with low voltage have sensitivity and susceptibility to EMI and many SMPS regulators in PSU and on MOBO around CPU must be earth bonded and well filtered for CM noise suppression.

Many peripherals with wall-warts are not earth-bonded and use isolated supplies may rely on earth bond connections to the host. (e.g. video)

Isolated ungrounded SMPS are notorious for RF leakage issues to secondary. e.g.USB peripherals with floating power and PC towers with earth bonded may fail to communicate on USB while laptops without charger pass.
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
2K
Replies
19
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K
Replies
7
Views
3K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 9 ·
Replies
9
Views
4K
  • · Replies 21 ·
Replies
21
Views
3K
Replies
61
Views
9K
  • · Replies 3 ·
Replies
3
Views
2K