Shunt resistor right application?

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
1 reply · 3K views
whodatnation
Messages
1
Reaction score
0
I have a 400A (125VDC) charger that feeds a battery bank and a few DC panels (critical). This poor design has the panels being fed from the high side of a 600A breaker that is between the charger and battery bank. I need to take the battery off line for a load test but the problem I'm going to have is when I reconnect the battery to the charger I will have a current surge coming from the 400A charger to the unenergized battery bank (approx. 350A). This will most probably cause a voltage drop in the DC panels which I CANNOT have (critical loads on panels). Will a proplerly sized shunt resistor between the disconnect switch and panels work for this situation?
 
Engineering news on Phys.org
Yes. I would not call it a shunt, I would call it a current limiting resistor. It needs to be sized for the ##I^2R## loss. Then it should be shorted once the surge has passed to remove it from the circuit.

I was thinking about an inductor for surge limiting, but no that would not work because the battery would be too slow to respond, making the surge last for seconds.