Slip test on salient pole machine

Click For Summary

Discussion Overview

The discussion revolves around the slip test on a salient pole machine, focusing on the behavior of voltage and current during the test. Participants explore the implications of constant impressed voltage versus observed voltage variations, the nature of the machine being tested, and the effects of rotor position on electrical measurements.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • Some participants question why the voltage measured varies despite a constant 3-phase voltage being applied across the stator, suggesting it behaves like a variable inductor circuit.
  • Others argue that during the slip test, the synchronous motor does not lock and functions as an induction motor, with the excited poles inducing an alternating EMF in the stator.
  • One participant highlights the relationship between network voltage and EMF, proposing that both create a standing wave voltage with nodes and antinodes, leading to voltage fluctuations.
  • Another participant seeks clarification on the apparent contradiction of constant impressed voltage versus fluctuating voltmeter readings, questioning what the voltmeter indicates.
  • Some participants note that while the impressed voltage remains constant, the observed voltage fluctuates due to varying current and impedance changes as the rotor moves.
  • There is mention of voltage regulation, with one participant explaining how output voltage can drop under load, suggesting that the power source's regulation affects the observed voltage.
  • Another participant discusses the relationship between armature terminal voltage and impedance drops, indicating that terminal voltages are not fixed due to variations in current with rotor position.
  • One participant reflects on their previous lack of awareness regarding impedance drops in leads, acknowledging that it was not covered in lectures.

Areas of Agreement / Disagreement

Participants express differing views on the nature of the machine during the slip test and the reasons behind voltage variations. There is no consensus on the interpretation of voltage behavior, with multiple competing explanations presented.

Contextual Notes

Participants mention the dependence of voltage readings on factors such as rotor position and impedance variations, indicating that assumptions about constant voltage may not hold in practice. The discussion also highlights the complexity of the electrical characteristics of the machine under test.

cnh1995
Homework Helper
Gold Member
Messages
3,489
Reaction score
1,163
In slip test, we provide a constant 3 phase voltage across the stator of the machine. Then why does that voltage vary? Its like a variable inductor circuit due to different air gap length but basically if the voltage impressed is kept constant, why does the voltmeter show variation?
Is it like changing the core of the inductor at its steady state. What will happen if I inserted iron core in the inductor when it reaches the steady state in a dc circuit?
 
Engineering news on Phys.org
In my opinion, during the slip test the synchronous motor did not locked in that means it is an induction motor still.

The excited rotated poles induce an a.c. EMF in the stator of a frequency of (1-s)*netfrequency.s=[(60*p*f)-rpmrotor]/(60*p*f) [the slip]

p=number of pole pairs.f=network frequency.

Both voltages -network voltage and EMF- will present a common standing wave voltage [nodes and antinodes] that means the voltage has a minimum and a maximum with s*f frequency.
 
Babadag said:
In my opinion, during the slip test the synchronous motor did not locked in that means it is an induction motor still.

The excited rotated poles induce an a.c. EMF in the stator of a frequency of (1-s)*netfrequency.s=[(60*p*f)-rpmrotor]/(60*p*f) [the slip]

p=number of pole pairs.f=network frequency.

Both voltages -network voltage and EMF- will present a common standing wave voltage [nodes and antinodes] that means the voltage has a minimum and a maximum with s*f frequency.
The machine is an alternator, not a motor. For the test purpose, it is run as an IM. And the rotor is not at all excited in this test.
 
Can you clear up this apparent contradiction ?

cnh1995 said:
we provide a constant 3 phase voltage across the stator of the machine. Then why does that (same? )voltage vary?
So is voltage constant or did it vary?

cnh1995 said:
if the voltage impressed is kept constant, why does the voltmeter show variation?

What voltage is the voltmeter indicating ? Must be different from the constant one that's impressed.U nder constant impressed voltage a current meter would vary with pole position.
Go back to that simple one turn machine in an earlier thread.
Magnetic path for D & Q axes is not the same , air gap is different.
 
The voltage impressed across stator is constant but the meter reads fluctuatiting voltage. I don't know how that happens. The current too fluctuates which I can understand. I don't understand the voltage part.
 
cnh1995 said:
The voltage impressed across stator is constant but the meter reads fluctuatiting voltage. I don't know how that happens. The current too fluctuates which I can understand. I don't understand the voltage part.

Hmmm you still insist that voltage is both constant and not-constant.

Perhaps this has to do with your question in another thread about 'regulation'.

Regulation in a voltage source, be it a power supply or an alternator or transformer or even a battery , is the change in output voltage over its full range of load current.
A regulated supply with nominal rating of ten volts & one amp, that puts out 10.0 volts unloaded and 9.9 volts when loaded to 1 amp,
has regulation Δvolts/nominal volts = 0.1 volts/10 volts = 1% .
Sooooo
Whatever power source you used to impress "constant volts " across the stator has some regulation.. That is, its output voltage drops by some percentage as you draw current from it.
If the volts it impressed across your stator were actually constant your voltmeter would have reported that.
Did your stator source have a dial or switch with numbers that you set ? That just sets what it tries to make ,

I assume you used a low voltage AC source for this test because applying full stator volts to a synchronous machine with its field open circuited should destroy the field winding.

You apply low AC volts to the machine then observe impedance as the rotor poles move under the stator poles. Impedance changes because the air gap of a salient rotor machine is not constant like a round rotor one. Try using Z = observed volts/observed amps

You use the same technique to find open rotor bars in a squirrel cage machine. Apply low voltage (to just one phase if a 3ph machine) and slowly rotate the shaft by hand while watching the ammeter.
Because the squirrel cage is a short circuit, a fair amount of stator current will flow so that's why you use low voltage. A broken rotor bar passing under the stator poles will make the ammeter dip because it's not a shorted turn like the good bars are.
You may notice a broken rotor bar in a running motor that's loaded,
it'll make the ammeter 'dip' sharply at slip frequency
 
  • Like
Likes   Reactions: cnh1995
actually ,voltage across armature is varied but supply voltage remains constant .
constant applied voltage -minimum impedance drop = armature terminal voltage ..
as in slip test current varies with respect to rotor position thus impedance drops are also not constant .
as a result armature terminal voltages are not fixed but these swings in voltage is so less because of low impedance drop in leads
 
kuldeep jain said:
in voltage is so less because of low impedance drop in leads
Right.
Back then, I was not aware of this impedance drop in the leads because it was not shown in the circuit diagram and our professor also didn't discuss it in the lecture.
I read a detailed explanation later in a reference book.
Thanks for your reply though!
And welcome to PF!:smile:
 

Similar threads

Replies
1
Views
3K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 6 ·
Replies
6
Views
2K
Replies
8
Views
2K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 2 ·
Replies
2
Views
5K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K