Static pressure in ducts and vessel

In summary, to find the pressure drop for the tank alone in a system where air is venting through a 10" duct at a rate of 2000 cfm, with a static pressure drop of 2” water column for every 100’ of length, and the duct opens to a 1000 cubic feet airtight vessel and exits through another 100’ of 10” duct, you can add up the pressure losses for each individual portion of the system. The pressure loss for the tank, assuming it is larger than the duct diameter, is only affected by the entrance and exit losses. More information can be found at the provided links.
  • #1
GordonC
1
0
If air is venting thru a 10" duct and there is a static pressure drop of
2” water column for every 100’ of length at 2000 cfm and the duct opens to a 1000 cubic feet airtight vessel and exits through another 100’ of 10” duct how can you find the pressure drop for the tank alone?
 
Engineering news on Phys.org
  • #2
Hi Gordon. You can add up the pressure losses for each individual portion of the system to come up with a total pressure loss. The loss for the tank, assuming it's large relative to the duct diameter, is only the entrance and exit losses. There's some discussion of that here:
http://utwired.engr.utexas.edu/che354/mom/pfit.ppt
and here:
https://www.physicsforums.com/showthread.php?t=105066&page=2
 
Last edited by a moderator:
  • #3


To find the pressure drop for the tank alone, we would need to calculate the total static pressure drop in the system and then subtract the pressure drop in the ducts.

First, we can calculate the total static pressure drop in the system by multiplying the static pressure drop per 100 feet (2" water column) by the total length of the ducts (200 feet). This gives us a total static pressure drop of 4" water column.

Next, we need to determine the pressure drop in the ducts. Since the air is venting through two 10" ducts, the total cross-sectional area is 200 square inches (2 x 10 x 10). We can use this information to calculate the velocity of the air, which is 2000 cubic feet per minute divided by 200 square inches, giving us a velocity of 10 feet per minute.

Using the Bernoulli's equation, we can then calculate the pressure drop in the ducts, which is equal to the dynamic pressure (0.5 x density of air x velocity squared) divided by the acceleration due to gravity. Assuming standard conditions, the density of air is approximately 0.075 pounds per cubic foot, and the acceleration due to gravity is 32.2 feet per second squared. Plugging in these values, we get a dynamic pressure of 0.002 pounds per square inch, which is equivalent to 0.048 inches of water column.

Therefore, the total pressure drop in the ducts is 0.048 inches of water column.

Finally, we can find the pressure drop for the tank alone by subtracting the pressure drop in the ducts (0.048 inches of water column) from the total static pressure drop in the system (4 inches of water column). This gives us a pressure drop of 3.952 inches of water column for the tank alone.

In summary, to find the pressure drop for the tank alone, we need to calculate the total static pressure drop in the system and then subtract the pressure drop in the ducts. This can be done by using the Bernoulli's equation and taking into account the velocity and cross-sectional area of the ducts.
 

What is static pressure in ducts and vessel?

Static pressure in ducts and vessel refers to the force exerted by a fluid at rest on the walls of a duct or vessel. It is the pressure that is present in the system even when there is no movement or flow of the fluid.

What causes static pressure in ducts and vessel?

Static pressure in ducts and vessel is caused by the weight of the fluid and the force of gravity acting on it. It is also influenced by the shape and size of the duct or vessel, as well as any obstructions or restrictions in the flow.

How is static pressure measured in ducts and vessel?

Static pressure in ducts and vessel is typically measured using a manometer, which is a type of pressure gauge that uses a column of liquid to indicate the pressure. It can also be calculated using Bernoulli's equation, which takes into account the fluid velocity, density, and elevation.

What is the significance of static pressure in ducts and vessel?

Static pressure in ducts and vessel is an important factor to consider in fluid flow systems, as it affects the performance and efficiency of the system. It can impact factors such as air flow, energy consumption, and system design.

How can static pressure in ducts and vessel be controlled or adjusted?

Static pressure in ducts and vessel can be controlled or adjusted by using devices such as dampers, valves, and fans. These can be used to regulate the flow of the fluid and alter the pressure in the system as needed.

Similar threads

  • Mechanical Engineering
Replies
33
Views
2K
  • Mechanical Engineering
Replies
24
Views
2K
  • Mechanical Engineering
Replies
7
Views
1K
Replies
1
Views
2K
  • Mechanical Engineering
Replies
3
Views
949
  • Mechanical Engineering
Replies
3
Views
1K
Replies
8
Views
2K
Replies
1
Views
2K
  • Mechanical Engineering
Replies
3
Views
2K
  • Mechanical Engineering
Replies
4
Views
3K
Back
Top