Tom.G
Science Advisor
Gold Member
- 5,661
- 4,503
You've got 99% of it right.kiki_danc said:And I understand that if I add a type 3 spd at equipment, the impedance of the 10 meter distance is what segregate it such that the SPD type 3 at equipment would only see the 1200 VPR output of the spd type 2 at breaker and not the full high voltage surge from the strike? If it sees only the 1200 VPR at the breaker then adding type 3 could bring it down to normal 220 volts (or 220.001 volts) VPR at equipment.
The type 3 at the equipment will bring the surge down to whatever its protection voltage is, and the type 3 SPD can have a lower energy rating than the type 2 in the breaker box.
ADDENDUM:
Hmm, we were typing at the same time. Your most recent post (#50) is for the case where you have the SPD in the breaker box but do NOT have one at the equipment to be protected. That's another reason to have an SPD as close to the equipment as possible, it eliminates those reflections and possible voltage doubling.
If needed, I'll post a sketch tomorrow (or maybe later today).
Cheers,
Tom