kiki_danc said:Here is the link I also shared in the same message https://zerosurge.com/normal-mode-v-common-mode/
After discussing with the electrician.. here are the complete facts.
The building service entrance is 3 phase with delta transformer... per phase is 120 volts.. but we never have any 120 volts outlets because 100% of our equipments are all 220 volts.. therefore my 220 volts in the outlets came from the line 1 and line 2 (or line 2 and 3 or 1 and 3) of the 3 phase.. in another floor.. the breaker is 3 phase. The one in the picture is admin breaker supplying only lights, cctv and security, hence only single phase needed and the design just tapped the phase 1 and 2 of the 3 phase service entrance power. With all these information.. my Spd type 2 that is line to ground won't be engaged at all because I don't have any equipments in the outlets that is 110 volts, right? If you agree, then I'll remove the existing SPDs and return them to supplier and buy a line to line SPD or delta SPD instead. Thanks.
Here's the breakers in my service entrance:
The front silver thing is the ground lugs. We don't have any neutral. If you will measure the voltage in any of the lines to the ground or even the enclosure, it's 120 volts.. but we never use 120 volts because all our equipments are 240 volts.. the one in the middle is the admin which connects to the panel you saw earlier. Therefore what I need are line to line SPD protecting 2 phases and not 1 phase to ground which is not utilized, right?? In the event there is surge in the line to line (phase 1 to phase 2), would it separately shunt to ground without any equipments actually connected to any phase and ground (or 110 volts we never used?)