Thermal conductivity in a heating system

Click For Summary
SUMMARY

The discussion focuses on calculating heat transfer in a domestic heating system using a radiator made of iron with a thermal conductivity of 80 W m-1 K-1. The radiator has a surface area of 1.5 m2 and a thickness of 2.0 mm, with water flowing at a rate of 0.12 kg s-1 and a temperature difference of 6.0 K. The correct method to determine the rate of heat supplied to the room is through the equation q/t = m c ΔT, leading to a calculated heat transfer rate of 3024 W, as opposed to the incorrect calculation of 360000 W.

PREREQUISITES
  • Understanding of thermal conductivity and its units
  • Familiarity with the specific heat capacity of water (4.2 x 103 J kg-1 K-1)
  • Knowledge of heat transfer equations, specifically q/t = m c ΔT
  • Basic principles of conservation of energy in thermal systems
NEXT STEPS
  • Study the derivation and application of the heat transfer equation q/t = m c ΔT
  • Learn about the impact of thermal conductivity on heat transfer in different materials
  • Explore the principles of steady-state heat transfer in heating systems
  • Investigate the effects of radiator design on heating efficiency
USEFUL FOR

Students studying thermodynamics, engineers designing heating systems, and anyone involved in optimizing thermal efficiency in domestic heating applications.

astri_lfc
Messages
7
Reaction score
0

Homework Statement




In a domestic heating system, a room is warmed by a 'radiator' through which water passes at a rate of 0.12kg s-1. The steady-state difference between the inlet and outlet temperatures of the water is 6.0 K.

The radiator is made of iron of thermal conductivity 80 W m-1 K-1 and has an effective surface area of 1.5 m2 with walls 2.0 mm thick.
(a) At what rate is heat supplied to the room?
(b) What is the mean temperature difference between the inner and outer surfaces of the radiator walls?
[Specific heat capacity of water = 4.2 x 103 J kg-1 K-1]

Homework Equations



a)q/t = k a ΔT / L
is it true use this equations?

b) q = m c ΔT

The Attempt at a Solution



a)
i put all the data to the formula, but the answer is 360000 w
my teacher give me the answer is 3024 w
which one is true?
 
Physics news on Phys.org
Your teacher is right. Show us your work.

Chet
 
k = 80
A = 1.5 m2
L = 2 x 10^-3
delta T = 6 K

q/t = 80 x 1.5 x 6 / (2x10^-3)

so q/t = 360000

what's wrong with thiss? :'(
 
What's wrong is that the 6 C is the temperature rise of the water in passing through the radiator, not the temperature difference across the thickness of the radiator iron. How much heat does the water lose per second in passing through the radiator?

Chet
 
oh i see
so shall i use q/t= m c deltaT ?
 
astri_lfc said:
oh i see
so shall i use q/t= m c deltaT ?
Yes, if m is the mass flow rate and q/t is the rate of heat transfer.

Chet
 
There are two parts to the question.

For part..

a) Apply conservation of energy. In steady state Power going into the rad = Power coming out. Power going in is (m/t)cΔT where (m/t) is the flow rate in kg/s^-1, c = specific heat capacity, and ΔT the temperature difference between input and output pipes (the output pipe isn't at absolute zero so some power is returned to the furnace/boiler)

b) A different equation will apply. Have a go first.
 
Actually there is a better way to explain equation in part a...

Power emitted to the room = Power into the rad - Power returned to the furnace

= mcTflow - mcTreturn
= mcΔT
 
okay thanks a lot! i have found the answer
 

Similar threads

  • · Replies 16 ·
Replies
16
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K
Replies
6
Views
924
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
1
Views
1K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 6 ·
Replies
6
Views
646
  • · Replies 4 ·
Replies
4
Views
2K