Three-phase power factor correction
Frank-95
Hello. I have a doubt regarding the following problem:
1. Homework Statement
Calculate capacitors' capacity to rephase (cos(φF) = 1) the load ZL
Circuit schematic of a three-phase delta load with three phase lines, a capacitor bank block labelled Capacitors, and load impedance labels ZL and a load value of 27 + 36j ohm.
The formula to calculate capacity in this case is:
CY = P(tan(φi) - tan(φF))/ωVrms2
or
CΔ = P(tan(φi) - tan(φF))/3ωVrms2
Firstly I converted the delta load in a star load:
ZLY = ZLΔ / 3 = 9 + 12 j Ω = 15e53,13j
The load phase is then 53,13. The final phase must be cos(φF) = 1 -> φF = 0.
In the image I posted I made an error: the pulsation isn't 50 Hz, the frequency is; hence pulsation ω = 100 π Hz.
Now I have initial and final phase, pulsation and I should apply the formula for finding capacitor, but the problem voluntarly do not give source voltages, so my doubt is: should I leave capacity dependent from power and root mean square voltage, or am I not considering something and I can make some more calculation? Thanks :)
I believe you don't need to convert delta to star here. To make the pf unity, the circuit must be seen as purely resistive by the source. So, inductive reactance per phase must be canceled out by capacitive reactance per phase, connected in parallel. I think you should just calculate the equivalent impedance per phase and equate it's imaginary part to 0.You will get Xc. Given the frequency, you can find C from it.
This is a way of pf improvement in a power system.