Calculate Currents & Power in 3-Phase Systems w/ Star-Connected Load

Click For Summary
SUMMARY

The discussion focuses on calculating currents and power in a balanced three-phase system with a star-connected load, specifically using a line voltage of 415V and impedances Za = 10 - j10, Zb = 10 + j10, and Zc = 0 + j8. Participants clarify the calculation of phase and neutral currents, emphasizing the importance of correctly determining the angle of Zc, which is 90 degrees due to its purely imaginary nature. The total power dissipation is derived using the formula P = Ea x Ia x cos(Φa) + Eb x Ib x cos(Φb) + Ec x Ic x cos(Φc), highlighting the significance of accurate angle measurements in power calculations.

PREREQUISITES
  • Understanding of three-phase electrical systems
  • Familiarity with complex impedance and phasor representation
  • Knowledge of power calculations in AC circuits
  • Proficiency in using vector diagrams for complex numbers
NEXT STEPS
  • Study the calculation of neutral currents in star-connected loads
  • Learn about the implications of angle measurement in complex impedance
  • Explore the use of vector diagrams for analyzing AC circuits
  • Investigate the impact of load imbalance on three-phase systems
USEFUL FOR

Electrical engineering students, professionals working with three-phase systems, and anyone involved in power system analysis and design.

Mathn00b!
Messages
9
Reaction score
0

Homework Statement


Hello, I am given the following problem.
A balanced three phase 4 wire supply has r.m.s. line voltage of 415V and supplies a star-connected load made of 3 impedances:
Za = 10 - j10; Zb = 10 + j10; Zc = 0 + j8;

Calculate the current phase and neutral currents, also the total power dissipation. [NOTE: Assume that Va is drawn vertically up, i.e. its phase angle is 90]

Homework Equations


I've used Vline = √3 x Vphase
Also, P = Ea x I a x cos(Φa) + Eb x I b x cos(Φb) + Ec x I c x cos(Φc)

The Attempt at a Solution


Please find the attached file, as my solution to the problem. As it could be seen the answer is quite different. In fact their answer is just the sum of the 1st two bits of the power, ignoring the last one. I assume they used cos(90) to get 0 and hence lower power. If this is the case, then the Zc should look like 8∠90° .
But isn't it found from the equation : Zc = √02 + 82 ∠tan-1 (8/0) ?

http://i1375.photobucket.com/albums/ag441/gl0ck1/StarLoad_zpslnhuotig.jpg
 

Attachments

  • StarLoad.jpg
    StarLoad.jpg
    37.2 KB · Views: 485
Last edited:
Physics news on Phys.org
Mathn00b! said:
Please find the attached file, as my solution to the problem.
Error: The requested attachment could not be found.
 
You must find the center voltage, En, at the center of the star-load.

Then:

Ia = ( Ea - En ) / Za , etc.

( I think? I cannot see if the center of the star-load is connected to neutral )
 
Last edited:
Strange, just sent it to one of my friends, he was able to open it. Will post a photobucket link just in a sec.
I am asked to find the neutral current, which could be found from the sum of all currents, no?
 
I've been able to open it now (error disappeared).
 
You may argue: If neutral is not connected to center of the star-load, then In = 0.
But I've found an error: Zc = ( 0 + j8 ) = 8 / 90°
 
Could you please, explain to me how you found it to be 8 ∠90°? What formula did you use? Isnt't it the same I used at the 1st post of the thread Zc = √02 + 82 ∠tan-1 (8/0) ? and tan-1 (0) = 0.
I presume it is connected since I've been asked to find it.
 
I'm not using any formula: Draw the vector ( 0 + j8 ) in the complex plane and measure the angle ( or you can see it by intuition ).

( Contrary: ( 8 + j0 ) = 8 / 0° )
 
The angle you've associated with Zc is incorrect. As a result the angle calculated for ##I_c## is incorrect.
The angle calculated for ##I_a## is incorrect.
 
  • #10
gneill said:
The angle you've associated with Zc is incorrect. As a result the angle calculated for ##I_c## is incorrect.
The angle calculated for ##I_a## is incorrect.
Yes you are right, it should be 135, but really don't understand the Zc's angle. Should I do it always like that? Drawing a vector, when the real part is zero?
 
  • #11
Mathn00b! said:
Yes you are right, it should be 135, but really don't understand the Zc's angle. Should I do it always like that? Drawing a vector, when the real part is zero?
It certainly can be helpful to sketch a vector for a complex value in order to get an idea of what the angle should be (such as the quadrant it lies in). But you should know that any purely imaginary number must have an angle of either + or - 90 degrees.
 
  • #12
Thank you both for the replies!
 

Similar threads

Replies
2
Views
4K
  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 2 ·
Replies
2
Views
6K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 2 ·
Replies
2
Views
5K
  • · Replies 6 ·
Replies
6
Views
2K