Summary:: I don't seem to see any problem with my work. But my final answer does not match the correct answer. (In number 3)
Here's my work
Here's my work
The discussion focuses on the calculation of total power consumed in a three-phase system. Participants emphasize the importance of accurately converting negative arguments to positive by adding 360 degrees instead of 180. The correct formula for calculating power is established as the real part of the sum of products: VR*conjugate(IR) + VY*conjugate(IY) + VB*conjugate(IB), with VR, VY, and VB defined as VR=IR*ZR, VY=IY*ZY, and VB=IB*ZB. Errors in the calculations, particularly regarding the value of IR, are highlighted as critical points for correction.
PREREQUISITESElectrical engineers, students studying power systems, and anyone involved in calculating three-phase power consumption will benefit from this discussion.
As mentioned, it's best if you type your work into the forum to make it more legible. Please see the LaTeX Guide link below the Edit window for more information on how to format math equations at PF. Thanks.Butterfly41398 said:I don't seem to see any problem with my work.
Following your entire calculation this it is not an issue. The only mistake it is wrong calculation of IR.Babadag said:I agree with the berkeman, of course. However, I manage to read your calculation. I still have to recalculate, but at first glance, I have a general observation: to convert the arguments from negative to positive you have to add 360 degrees and not 180.