Understanding AC Step Up Transformers: Common Issues and Solutions

  • Thread starter Thread starter FenderStrat62
  • Start date Start date
  • Tags Tags
    Transformer
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
10 replies · 2K views
FenderStrat62
Messages
4
Reaction score
0
I've been running some tests on some simple AC step up transformers, and I can't seem to justify something to myself:

I hook up 12 VAC to the primary coil, but the voltage on the coil is actually more like 1 VAC, when measured with a voltmeter. It's not an issue with the supply--it puts out 12 VAC just fine when not hooked up to my transformer.

What simple concept am I not remembering? Something to do with the impedance of the inductor, maybe?
 
Engineering news on Phys.org
If the secondary is open then it could mean that you have a bad transformer. If the secondary has a load on it then it could mean that the power requirement of the load exceeds the power capability of the power supply. Many power supplies will foldback when overloaded.
 
The secondary had a 1 megaohm resistor for the load, since that's the closest resistor I had laying around. So, there wasn't much power being drawn.
 
Are you sure your power supply is AC only? If it is AC only then it sounds like you have a bad transformer.
 
FenderStrat62 said:
I've been running some tests on some simple AC step up transformers, and I can't seem to justify something to myself:

I hook up 12 VAC to the primary coil, but the voltage on the coil is actually more like 1 VAC, when measured with a voltmeter. It's not an issue with the supply--it puts out 12 VAC just fine when not hooked up to my transformer.

What simple concept am I not remembering? Something to do with the impedance of the inductor, maybe?

How and where are you taking the measurement?

CS
 
Turtle: I trust that the power supply is AC only, as that's never been an issue before. I could hook it up to an oscilloscope next time I'm in the lab to make sure. I didn't take DC readings, so I don't know what I'd read there.

Also, it would really surprise me if it was a bad transformer. All the transformers I tested acted this way, and the voltage ratios were all to spec, even at the lower-than-expected voltage.

Stewart: I've got the 12VAC leads hooked up to the primary side from an AC power supply, and a 1 megaohm resistor hooked up to the secondary side. I'm using a pair of multimeters and measuring VAC at the legs of primary and secondary side of the transformer.
 
FenderStrat62 said:
Turtle: I trust that the power supply is AC only, as that's never been an issue before. I could hook it up to an oscilloscope next time I'm in the lab to make sure. I didn't take DC readings, so I don't know what I'd read there.

Also, it would really surprise me if it was a bad transformer. All the transformers I tested acted this way, and the voltage ratios were all to spec, even at the lower-than-expected voltage.

Stewart: I've got the 12VAC leads hooked up to the primary side from an AC power supply, and a 1 megaohm resistor hooked up to the secondary side. I'm using a pair of multimeters and measuring VAC at the legs of primary and secondary side of the transformer.

I mean where are you reading the 1 VAC...across the primary terminals or the secondary terminals?

CS
 
The primary is roughly 1 VAC. It's not exactly that, just ball park.
 
If you have a transformer that normally converts 110 volts to 12 volts, then you can use that transformer backwards by feeding it with 12 volts AC to get 110 volts out.

But, if it previously gave 4 volts out then you can't put 12 volts on it and expect to get 330 volts out. The problem is that the smaller winding won't have enough inductance and will draw too much current from the 12 volt supply.

Do you know what the rated voltage is for each of the windings on this transformer?