Utility Metering Current Transformer

Click For Summary

Discussion Overview

The discussion centers around the operation of current transformers (CTs) used in electric utility metering, specifically in relation to high voltage systems. Participants explore how CTs measure current while isolating measuring instruments from high voltages, and the implications of their design and operation in both high voltage and low voltage applications.

Discussion Character

  • Technical explanation
  • Conceptual clarification
  • Debate/contested

Main Points Raised

  • One participant questions whether the CT is stepping down current or voltage, noting the confusion around the relationship between voltage and current in transformers.
  • Another participant clarifies that the primary of the CT is the high voltage conductor, which acts as a single turn, while the secondary has multiple turns, providing isolation from high voltages.
  • A participant expresses a misunderstanding about the primary potential seen by the CT, realizing it only sees the voltage drop across the conductor rather than the full rated potential.
  • Discussion includes the rating of CTs, with one participant explaining that typical ratings are 1A or 5A for secondary current, and provides a formula relating primary and secondary currents to the number of turns.
  • Concerns are raised about the dangers of open-circuiting the secondary, which could lead to dangerously high voltages if the CT behaves like a voltage transformer under such conditions.
  • Another participant elaborates on the consequences of open-circuiting, discussing the increase in magnetizing flux and the potential for saturation or damage to the CT.
  • A participant illustrates the relationship between primary and secondary currents and the importance of loading the secondary with a resistor to prevent high no-load voltages.

Areas of Agreement / Disagreement

Participants express various understandings of how CTs operate, particularly regarding the relationship between voltage and current. There is no consensus on certain aspects, such as the exact nature of the voltage seen by the CT or the implications of open-circuiting the secondary.

Contextual Notes

Participants highlight limitations in understanding the voltage seen by the CT primary and the effects of loading on the secondary circuit. There are unresolved questions regarding the full implications of the CT's operation under different conditions.

rollingstein
Messages
644
Reaction score
16
The electric utility has a digital wattmeter that seems to be measuring the power usage at the high voltage side of our distribution transformer (11 kV - 420 V 3 phase, 250 kVA) via a Current Transformer.

How exactly does this work? Specifically, what I'm confused about is that transformers generally obey a VxI=const. relationship (barring losses). So is this CT stepping down the current or is it stepping down the voltage?

Wikipedia says this:

"When current in a circuit is too high to apply directly to measuring instruments, a current transformer produces a reduced current accurately proportional to the current in the circuit, which can be conveniently connected to measuring and recording instruments. A current transformer isolates the measuring instruments from what may be very high voltage in the monitored circuit. "​

This sounds to me like they are saying it is reducing the current as well as reducing the Voltage. How can a transformer do both at once? What gives?
 
Engineering news on Phys.org
The voltage of the conductor referenced to Earth is 6500 V. But the voltage between any two close points along the conductor is (almost) zero

The primary of the CT is the HV conductor itself, which is essentially one turn. The Secondary has many turns.

The CT is placed along the conductor (the primary), so what it is doing is 'isolating' the secondary small wiring from the high voltages of the circuit.
CTs are also used in LV metering where the current is too high (>100A) for direct metering.It works just like your clip-on ammeter.
 
Last edited:
Thanks @William White!

So my confusion was I was assuming the CT-primary sees the rated primary potential whereas in reality it only sees a small potential just the drop across the conductor for however large the CT it.

In any case, given that the primary is one turn (in effect) and the secondary many turns, the CT will be a step-up TX in terms of Voltage? i.e. Current reduces?

i.e. If the current of the distribution TX primary were 10 A then the CT will actually see less than 10 A etc. depending on how many turns?
 
most CTs for power systems protection are rated at 1A or 5A.

So you will see written on the side of the CT (or on the protection relay) 100:5 ; which means 100A of primary current give 5A secondary current

so you have

Is = Ip Np / Ns

where Is is secondary current, Ip is primary current Np is primary tunrs and Ns is secondary turns

the voltage across the secondary circuit is just ohms law
Vs = Is Rs

because Is is small (just 1A or 5A) and Rs (the resistance of the secondary circuit) is small (milli ohms) the voltage is small.

This is where it is essential not to open circuit the secondary! If you do do that the CT becomes a voltage transformer and you get huge voltages across the CT secondary.
If your primary voltage is 6400V and your CT has 100 turns on the secondary, then if the open circuit CT voltage:
Vs = 6.4kV x 100 = 640 kV!
 
Last edited:
William White said:
This is where it is essential not to open circuit the secondary! If you do do that the CT becomes a regular step-up voltage transformer and you get huge, lethal voltages across the CT secondary.
If your primary voltage is 6400V and your CT has 100 turns on the secondary, then if the open circuit CT voltage:
Vs = 6.4kV x 100 = 640 kV!

Hmm...I don't think I get this part.

Like you explained in your earlier post shouldn't it act like a step-up but the primary voltage shouldn't be the full 6400 V but only " the voltage between any two close points along the conductor"? After all the CT primary winding isn't seeing the conductor-to-earth full PD? Only the primary Distribution Transformer Winding sees this?
 
If you open circuit the secondary there is a huge increase in the magnetising flux in the secodary winding which induces a voltage in the secondary winding. In theory, an open circuit has resistance of infinity (it doesn't in practice because the air is a conductor, so there is no true purely open circuit - even the vacuum in a VCB is not an infinite resistance); so you might think the voltage would increase without limit. What happens is the flux increases until the secondary is saturated or the thing blows up. It is one reason why you should never ever put any protection (fuses/breakers etc) in the secondary circuit. If the protection operated, the circuit is open and you get very high voltages.
 
Last edited:
  • Like
Likes   Reactions: dlgoff
The secondary of a CT is loaded by a low valued resistor.

Say that N1 = 1 , I1 = 100A , N2 = 1000 , then I2 will be 100A/1000 = 100 mA. Now load the secondary with a 10Ω resistor and you will get a voltage = 1V. That's the one to be measured.

You may never install a CT without having the secondary properly loaded due to very high no-load voltage.

The core of the CT will not be saturated because N1*I1 ≈ N2*I2.
 
Last edited:

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 47 ·
2
Replies
47
Views
5K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 6 ·
Replies
6
Views
2K
Replies
4
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 17 ·
Replies
17
Views
7K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 14 ·
Replies
14
Views
4K
  • · Replies 6 ·
Replies
6
Views
5K