Voltage, real reactive power question

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
4 replies · 2K views
debwaldy
Messages
34
Reaction score
0

Homework Statement



A 33 kV single phase generator is supplying a customer a load through a cable with an impedance j2 ohms

a.What voltage would the customer experience if rated current of 500 A is drawn at power factor of unity at the customer end?

b. How much active and reactive power would be provided by the generator?


Homework Equations


V = IZ
P = IV

PF = P/S = IV cos phi

The Attempt at a Solution



Part a: Do I need to find the total impedance using V = IZ equation, and then calculate the impedance of the customer load by subtraction, and then sub this impedance of the load back into the V = IZ formula to find the customer voltage?

Or is the customer voltage simply 33 kV?

I am very confused by terminology?

Any help much appreciated
 
Physics news on Phys.org
Are you trying to solve this using RMS Values ?
 
we have been told to assume that all voltage values given are rms voltage values so we don't need to worry about that...
 
Would it be possible to just say that P = S and hence the voltage at the customer end will also be 33kV?
 
You have a circuit with three elements, a voltage source of 33kV, an impedance of j2 ohms, and another impedance which is assumed to be purely resistive. That is, the generator supplies 33kV to some network, what the customer sees, you don't know.

Equivalent Z is Z=R+2j, that is 33kV = (R+2j)*500A, which yields the load impedance. The voltage drop is then 33kV*R/(R+2j).

/M