The forum discussion centers on the calculation of winding resistance for a 415V to 11 kV transformer rated at 200 kVA, specifically addressing the maximum secondary winding resistance to achieve 2% voltage regulation at unity power factor. The primary winding resistance is given as 10 mΩ, and the calculations involve the formula R'p = Rp + n²·Rs, where Rp is the primary winding resistance and n is the turns ratio. Participants confirm the correct approach to the problem while addressing concerns about the units in the equations and the accuracy of their calculations.
  • Understanding of transformer voltage regulation concepts
  • Familiarity with electrical engineering formulas, specifically R'p = Rp + n²·Rs
  • Knowledge of turns ratio calculations in transformers
  • Basic proficiency in Ohm's law and electrical unit conversions
  • Study transformer voltage regulation calculations in detail
  • Learn about the implications of winding resistance on transformer performance
  • Explore the derivation and application of transformer equations
  • Investigate common errors in electrical engineering calculations and how to avoid them
Electrical engineering students, professionals working with transformers, and anyone involved in designing or analyzing transformer performance and efficiency.
Gremlin
A 415V to 11 kV transformer has a rating of 200 kVA. The winding resistance and leakage reactance when referred to the primary are 0.014 Ω and 0.057 Ω respectively.
(b) In designing a particular 415V to 11 kV, 200 kVA transformer, the primary winding resistance is to be 10 mΩ. Find the maximum winding resistance of the secondary winding if the transformer is to have 2% regulation at unity power factor.
Voltage Regulation ≈ (VA Rating / V12) x R'p x 100
n = N1 / N2 = E1 / E2
R'p = Rp x n2 Rs
Voltage Regulation = 2%
VA Rating = 200000
V1 = 415
V2 = 11000
Rp = 0.01
Cosθ = 1
2 ≈ (200000 / 4152) x R'p x 100
2/100 ≈ 1.161271 x R'p
0.02 / 1.161271 ≈ R'p
R'p ≈ 0.01722
E1 / E2 = 415/11000 = 0.037727
0.01722 = 0.01 x 0.0377272 x Rs
0.01722 / 1.42333 x 10-3 = Rs
Rs = 1209.84Ω
I'm sure I'm wrong, but am i in the correct ball park in the way I'm going about answering the question?
Thanks.
The maths is wrong but I'm happy I've got the right idea - and the right answer when the maths is corrected.
R'p = Rp x n2 Rs
That expression for R'p looks a bit odd. The units don't make sense (Ohms squared on the right hand side).
n = N1/N2 = E1/E2
Is n = V1/V2? In other words, E1 = V1? E2 = V2?
If they are, n = 415/11000 = 0.0377
Is this correct?
James Goodchild said:
n = N1/N2 = E1/E2
Is this correct?
Yes, that's correct. Although sometimes you'll see an author use V2/V1 instead, as it yields values greater than 1 (a convenience only) for step-up transformer situations. Formulas employing 'n' will be adjusted accordingly, using 1/n in place of n.
Thank you Gneill. I was not sure, as the winding resistance and leakage reactance connected in series with the primary winding suggest that V1 is not equal E1.
I was also instructed to use the above formula (OP) by my tutor; however I'm somewhat concerned that the R'p equation looks odd.
I have completed the calculations as instructed and found b) = 1210.19 Ohms (2 dp), i had not questioned my answer until i came across this post. Can anyone confirm if there is an error in the R'p = Rp x (n^2 x Rs) formula so i can go back and re-do the question?
Thanks, Kate
Thanks, Kate
The units there don't match, so it can't be right.
The total winding resistance referred to the primary side would be Rp + n²·Rs
Hi, I have a value for Rs of 1.488 ohms, Could somebody please tell me if I am wildly incorrect?
Many thanks
hi i am new to the forum and trying to complete the electrical and electronic engineering course but the learning material provided does not seem to provide adequate knowledge to complete some of the questions being asked. I rearranged the formula R'P = RP + n^2 * RS to RS = R'P / (RP + n^2) which resulted in RS = 1.50744 ohms but with so many values being suggested on the forums I am doubting the result. cheers
Hi casper12.
In future, please start a new thread for your question, unless it is a follow-on to an earlier thread dealing with the same question. This saves readers having to wade through old unrelated posts before reaching yours.
[emoji422] If in doubt of your re-arrangement, you can always check to confirm it is correct!
Here's how: Take any convenient arbitrary value for RP, RS and n, and evaluate what those values would make for R'P in your first equation. Now, using these values work out what the right-hand side of your second equation would be.