What are these transformer looking like things?

  • Thread starter Thread starter Nathi ORea
  • Start date Start date
  • Tags Tags
    Transformer
Click For Summary
SUMMARY

The discussion centers on identifying a peculiar electrical device, which is likely an enclosed disconnect switch or a recloser, used for maintenance and fault management in power distribution systems. Participants noted that the device allows linemen to operate it safely from the ground using an extended handle. The recloser is designed to automatically open and close circuits in response to faults, particularly in rural areas where momentary faults are common due to wildlife or falling branches. The conversation also highlights the possibility of three-phase reclosers being utilized in specific power systems.

PREREQUISITES
  • Understanding of electrical distribution systems
  • Familiarity with reclosers and their operational mechanics
  • Knowledge of fault management in power lines
  • Awareness of the differences between single-phase and three-phase systems
NEXT STEPS
  • Research "Recloser operation and programming" for detailed insights on settings and configurations
  • Explore "Enclosed disconnect switch applications" to understand their role in maintenance
  • Investigate "Three-phase reclosers" and their advantages in power distribution
  • Learn about "Fault management techniques in rural power systems" to enhance understanding of common issues
USEFUL FOR

Electrical engineers, utility workers, and anyone involved in power distribution and maintenance will benefit from this discussion, particularly those seeking to understand the functionality and application of reclosers and disconnect switches.

Nathi ORea
Messages
82
Reaction score
22
TL;DR
I have seen these transformer like things on the higher voltage powerlines when I go to regional areas in NSW (Australia) and I was wondering what they are?
They couldn't be transformers because they are not connected to any other wires.
Would love any insights.
IMG_2833.jpeg
IMG_2836.jpeg
IMG_2835.jpeg
IMG_2844.jpeg
 
Engineering news on Phys.org
That is strange looking. Note the pole that runs partway down toward the ground.

My guess is that it is an enclosed disconnect switch. With the power off, a lineman can reach up to that pole and open/close the switch.

Why disconnect? Mostly for maintenance purposes.

Here are pictures of open-air versions of disconnects.

1671622673494.png
1671622694156.png
 
  • Like
Likes   Reactions: sophiecentaur, DaveE, nsaspook and 1 other person
anorlunda said:
That is strange looking. Note the pole that runs partway down toward the ground.

My guess is that it is an enclosed disconnect switch. With the power off, a lineman can reach up to that pole and open/close the switch.

Why disconnect? Mostly for maintenance purposes.

Here are pictures of open-air versions of disconnects.

View attachment 319142View attachment 319143
Cool! Thanks so much for that

is the pole running down the pole to ground it is they want to turn it off?
 
I think that pole is just an extended handle. It can be reached with a hand-held pole from the ground. If it went all the way to the ground, they would need a fence to prevent ordinary people from fooling with it.
 
  • Like
Likes   Reactions: Nathi ORea, sophiecentaur and Nik_2213
Agreed - looks like a sectionalizer, possibly with vacuum interrupters allowing it to offer protection, as well as remote connection / disconnect control - as well as manual isolation.
 
  • Like
Likes   Reactions: Nathi ORea, BvU and Nik_2213
That may be a recloser.
If you live in a rural area, you have probably noticed the power blinking off for a few seconds.
The most common causes of faults on rural distribution lines are momentary faults caused by rodents or birds shorting the line to ground or by falling tree branches. The second most common cause of faults is either a bad short on a secondary circuit or a burned out transformer.

The recloser instantly opens the circuit in the event of any over-current and then recloses a few cycles or seconds later. If the fault is still present the recloser will open again after a few cycles. This may be repeated three times, giving the rodent or tree branch a chance to fall away from the line and clear the fault.

If the fault does not clear after three tries, it may be a shorted distribution transformer. The recloser will then close in for a longer time to try to clear the local fuse at he transformer.
After a total of five tries, the recloser will remain open until manually reset.
It has been a long time and I forget the typical recloser time settings. In any event the operation is controlled by a micro computer and the system engineer is free to program it any way he chooses.

BUT
Reclosers are typically single phase and that looks like a three phase unit.
There are some power systems that have a tendency to back feed into a fault from either a delta secondary or from a transformer that magnetically develops a phantom delta.
These systems would use three phase reclosers.

anorlunda may be correct and that may be an interrupter of some sort.
The odds are probably 90/10 in favour of Anorlunda's suggestion.
 
waross said:
That may be a recloser.
If you live in a rural area, you have probably noticed the power blinking off for a few seconds.
The most common causes of faults on rural distribution lines are momentary faults caused by rodents or birds shorting the line to ground or by falling tree branches. The second most common cause of faults is either a bad short on a secondary circuit or a burned out transformer.

The recloser instantly opens the circuit in the event of any over-current and then recloses a few cycles or seconds later. If the fault is still present the recloser will open again after a few cycles. This may be repeated three times, giving the rodent or tree branch a chance to fall away from the line and clear the fault.

If the fault does not clear after three tries, it may be a shorted distribution transformer. The recloser will then close in for a longer time to try to clear the local fuse at he transformer.
After a total of five tries, the recloser will remain open until manually reset.
It has been a long time and I forget the typical recloser time settings. In any event the operation is controlled by a micro computer and the system engineer is free to program it any way he chooses.

BUT
Reclosers are typically single phase and that looks like a three phase unit.
There are some power systems that have a tendency to back feed into a fault from either a delta secondary or from a transformer that magnetically develops a phantom delta.
These systems would use three phase reclosers.

anorlunda may be correct and that may be an interrupter of some sort.
The odds are probably 90/10 in favour of Anorlunda's suggestion.
Thanks so much for your answer waross.

It seems and amazing coincidence that I saw this while walking my dog just last week and wondered what it was.

IMG_4067.jpeg

After a bit of Googling around I found out it was a recloser. I spent a bit of time learning about what they actually did too. You explanation is kinda how I understand how they work now, so that validates my efforts.. lol

On another forum they were pretty confused about that post too, but one of them emailed a person they knew in Australia, and she sent me this link.

https://insulect.com/products/gas-insulated-load-break-switches

so... there you go.. it is a disconnecting thingy (whatever they're called).

I think it must be just an Australian type.

I really appreciate your response.
 
  • Like
Likes   Reactions: Nik_2213, Tom.G and berkeman

Similar threads

  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 8 ·
Replies
8
Views
1K
Replies
10
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 21 ·
Replies
21
Views
2K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 18 ·
Replies
18
Views
5K