sophiecentaur said:The system has a vast 'smoothing capacity' hanging on it, in the form of all the other consumers.
You can monitor the net effects of smoothing (including voltage effects) and if the ability of power plants to respond in your own home. Just sample and display frequency.
If you don't want to do it at home, there are Web sites that let you do it. I'll bet that Jim could find such a site for us.
I'll give you a magic number 1/8. Take the instantaneous unbalance between grid generation and load (including any effects of voltage), multiply by 1/8 and you get rate of change of frequency. Express power as percent of the total capacity (not current load but rated capacity) of all generators on the grid. Expressed frequency as percent.
Suppose we had a grid with 100GW of capacity online and a base frequency of 50 hertz, then an unbalance of 1GW will cause 1/8 %/second or 1/16 hertz /second rate of change of frequency.
Working backward, watching frequency in real time, differentiate and multiply by 8 and you can observe the real time unbalance in the grid. You should see that typical unbalance is on the order of .005% on a big grid.
On small grids, such as on a self sufficient island, it is much worse. I vacationed once on Grand Canary, and I could hear the refrigerator motor speed changing up and down.
Sophie, is the UK synchronized to Europe?
Watch frequency long enough an you will see a major event like a 1GW plant tripping. Correlate that with news reports, and you can learn which plant tripped.
p.s. The magic number 8 has to do with the inertia of turbine-generators.