What if a 60Hz Transformer is Connected to a 6Hz Source?
  • Thread starter Thread starter glasgowkizz
    Transformer
Connecting a 60Hz transformer to a 6Hz source would cause the transformer core to saturate, leading to excessive current flow primarily limited by winding resistance. The reactance of the transformer would significantly decrease, resulting in a current increase to approximately ten times the normal level. This excessive current could trip circuit breakers or potentially cause the transformer to burn out or explode. The low frequency drastically reduces inductive reactance, allowing for heavy current draw that can lead to damage. Overall, operating a 60Hz transformer at 6Hz is highly dangerous and likely to result in failure.
glasgowkizz
What would happen if a transformer designed for operation on 60Hz were connected to a 6Hz source of the same voltage?
The core would saturate (magnetic) and the current would be limited mainly by the winding resistance. Hence it would either trip a circuit breaker or burn out within a very short time.
It would probably blow up.
The primary of a transformer has inductance and this is what stops the transformer taking too much current when it is connected to a source of voltage.
The reactance of the transformer primary is given by XL = 2 * pi * F * L
where F is the frequency and L is the inductance.
Reactance is like AC resistance.
If you reduce the frequency to 6 Hz then the reactance will drop to 10 % of what it was before.
So, the current will rise to 10 times what it was before, at least. Mainly it will be limited by the resistance of the wire on the primary winding which is usually very low.
since frequency is 10 times less hence the inductive reactance of transformer.
so transformer would draw heavy current, may damage.
Thanks guys!
(Thread moved to Homework Help, but too late...)
Thread 'Have I solved this structural engineering equation correctly?'
Hi all, I have a structural engineering book from 1979. I am trying to follow it as best as I can. I have come to a formula that calculates the rotations in radians at the rigid joint that requires an iterative procedure. This equation comes in the form of: $$ x_i = \frac {Q_ih_i + Q_{i+1}h_{i+1}}{4K} + \frac {C}{K}x_{i-1} + \frac {C}{K}x_{i+1} $$ Where: ## Q ## is the horizontal storey shear ## h ## is the storey height ## K = (6G_i + C_i + C_{i+1}) ## ## G = \frac {I_g}{h} ## ## C...