B Why did making the recovery tank cold expedite recovery of refrigerant?

AI Thread Summary
Placing a recovery tank in ice during refrigerant recovery expedites the process by lowering the temperature and pressure inside the tank. As the refrigerant expands, it cools, which reduces the pressure of the gas in the tank, allowing more refrigerant to flow in. This is the opposite of charging refrigerant from a tank, where warm water is used to increase pressure and facilitate flow. The cooling effect enhances the condensation of gas inside the recovery tank, creating a vacuum that draws in more refrigerant. Thus, using ice significantly accelerates the recovery process.
sevensages
Messages
161
Reaction score
34
TL;DR Summary
Why did making the recovery tank cold expedite the recovery of refrigerant?
Many years ago, I was a student in a HVAC program at a technical college. Sometimes when I and the other students were recovering refrigerant out of an air conditioner into a recovery tank, we would get ice from the ice machines and fill up a tub with ice, and then we would put the recovery tank in ice as we recovered the refrigerant. The placement of the recovery tank in a tub of ice would expedite the migration of the refrigerant from the air-conditioner to the recovery tank. Why did the placement of the recovery tank in ice expedite the migration of the refrigerant from the air-conditioner to the recovery tank?
 
Science news on Phys.org
When any gas gets expanded, it tends to cool down and take energy from its surroundings.
As temperature of the liquid-gas mix is reduced, so is the pressure inside the tank, because its volume is constant and also because the pressure of evaporation gets reduced at that reduced temperature.

That is why, when charging any refrigerant into an air conditioner from a storage tank, the tank naturally cools down due to the refrigerant expansion.
Placing that tank into a bucket with warm water, expedites the injection of refrigerant into the equipment.

The process that you describe is the opposite to the one described above.
The vacuum pump tends to increase the pressure and temperature of the gas that is transferring from the AC equipment into the tank.

As you encourage the condensation of that gas inside the recovery tank, the pressure of the gas phase gets drastically reduced, making room for more gas to come inside the tank.
Hence, the cooler the faster the recovery process.
 
I need to calculate the amount of water condensed from a DX cooling coil per hour given the size of the expansion coil (the total condensing surface area), the incoming air temperature, the amount of air flow from the fan, the BTU capacity of the compressor and the incoming air humidity. There are lots of condenser calculators around but they all need the air flow and incoming and outgoing humidity and then give a total volume of condensed water but I need more than that. The size of the...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...