Why Does Smaller Pipe Diameter Reduce Equivalent Length in Elbows?

Click For Summary
Smaller pipe diameters result in shorter equivalent lengths for elbows due to the dynamics of fluid flow, where larger diameters experience more turbulence and mixing at the bend. Empirical data suggests that a 2.5" diameter elbow can have an equivalent flow to a 1.6" straight pipe, indicating that flow characteristics differ significantly with diameter. The equivalent length of a 90-degree elbow in carbon steel piping is typically longer than that of smaller diameters, which affects pressure drop calculations. Understanding these relationships is crucial for accurate system design and pressure loss assessments. The discussion emphasizes the importance of empirical studies in determining these hydraulic characteristics.
smoque
Messages
6
Reaction score
0
can someone explain to me why it seems that the smaller the diameter of pipe bend (i.e. 90 degree elbow = 30D) the shorter its equivalent length becomes? for 1.5" diameter = 45" equivalent length while 2" diameter = 60" length. does this mean 1.5" diameter 90 degree elbow has less friction than the 2"? does not make much sense to me

thanks
 
Engineering news on Phys.org
Larger pipe diameters have more flow going through it which hit the "wall" created by the 90. There is more mixing.
There are many reasons, and the fact is a lot of it is empirical data.

It has a bit to do with the amount of flow going around the bend that is laminar and the amount that is turbulent.
 
i have read somewhere on the net that a 2.5" diameter of 90 degree elbow have equivalent flow of 1.6" straight pipe of same length as the bend.

any way to figure out how the statement above is derived?
 
This is generally an empirical study. In carbon steel piping, a normal 90 elbow of 2.5" pipe is equivalent to 9.3 ft of straight pipe.

So if you have 40ft of pipe, then a 90, then 40 ft. You have an "equivalent length" of 40+40+9.3, or 89.3 ft of pipe. You use this along with the friction factor of the pipe material to determine the pressure drop.

Here is a website that shows you some Leq's (equivalent lengths) based on the steel pipe's nominal diameter:http://www.delftaerospace.org/en/organisation/departments-and-chairs/space-engineering/space-systems-engineering/expertise-areas/space-propulsion/design-of-elements/feed-systems/feed-systems-b/ is one that shows you the Leq/D so you can multiply the number by the pipe diameter (in feet) and get the equivalent length

Here Is a site that kind of shows you the math involved
 
Last edited by a moderator:
Had my central air system checked when it sortta wasn't working. I guess I hadn't replaced the filter. Guy suggested I might want to get a UV filter accessory. He said it would "kill bugs and particulates". I know UV can kill the former, not sure how he thinks it's gonna murder the latter. Now I'm finding out there's more than one type of UV filter: one for the air flow and one for the coil. He was suggesting we might get one for the air flow, but now we'll have to change the bulb...

Similar threads

  • · Replies 3 ·
Replies
3
Views
6K
  • · Replies 20 ·
Replies
20
Views
5K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 10 ·
Replies
10
Views
6K
  • · Replies 20 ·
Replies
20
Views
10K
Replies
4
Views
2K
  • · Replies 15 ·
Replies
15
Views
3K
  • · Replies 3 ·
Replies
3
Views
16K
Replies
13
Views
4K
  • · Replies 7 ·
Replies
7
Views
7K