Wiring 3/4 HP Submersible Well Pump - Is #10 OK?

  • Thread starter Thread starter Cawagner
  • Start date Start date
  • Tags Tags
    Pump Wiring
AI Thread Summary
Using #10 wire for a 3/4 HP submersible well pump is acceptable as long as the breaker does not exceed 20 amps, especially if #12 wire would have sufficed for the entire run. It's crucial to consider local electrical codes, which can vary significantly by location. Consulting a licensed electrician is recommended to ensure compliance and safety. If the motor's specifications indicate it draws an appropriate amount of current, the wiring setup should be adequate. Always verify the motor's amp draw against the circuit requirements for optimal performance.
Cawagner
Messages
1
Reaction score
2
TL;DR Summary
mixing 2 wire gauges for submersible well pump
3/4 hp submersible well pump with #12 wire at top of casing from pump. I had a senior moment and wired from the panel to the pressure switch and switch to top of casing with #10. I am thinking I am ok as long as the breaker never exceeds 20 amps. Just want to make sure. Thanks.
 
Engineering news on Phys.org
Electrically, if #12 copper would have been sufficient for the entire run, then a combination of #10 and #12 copper would also be electrically sufficient.

However, different cities/states/countries have different electrical codes. I would suggest you consult with a licensed electrician.

If we are talking 120V, then a 20Amp breaker is OK for a 3/4 HP motor is this kind of application. According to the motor labeling or the manual, how many amps does the motor draw?
 
  • Like
Likes berkeman, jim mcnamara and russ_watters
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...