A room has a need for 2000W for an outside temp of -20 C. A radiator with this capacity is installed and recieves water at 90 C, which exits at 70 C. But because of some error only 40% of the intended water amount flows through the radiator. The water temp delivered to the radiator is adjustet according to the outside temp, and is 60,5 C when outside temp is 0 C. What will the temp in the room be at an outside temp of 0 C ?

What I don't get is how to incorporate the fact that the water delivered to the radiator is adjustet according to the outside temp. How do I put this into my calculations?
Phys.Org News Partner Science news on Phys.org
FIXD tells car drivers via smartphone what is wrong
Team pioneers strategy for creating new materials
Team defines new biodiversity metric
Gokul43201
#2
Feb18-05, 07:55 PM
Emeritus
Sci Advisor
PF Gold
Gokul43201's Avatar
P: 11,155
This question is just bad. It doesn't provide anywhere near enough data and it's poorly framed.
minger
#3
Feb21-05, 07:18 AM
Sci Advisor
P: 1,498
Agreed. I think you will need at least a flow rate of the water, not just 40% of original flow rate. Given that you have a flow rate, you can find heat flow based on
Q(dot) = m(dot)Cp(T2-T1)
If the change in temperature is being changed constantly according to the outside temp, I assume some smart guy here could set up an integral or something....I'm not sure where to start based on the information given though.

Artman
#4
Feb23-05, 04:20 PM
P: 1,591
Radiator calculations

I work in English units and I am not sure of the conversions, but here is a start:

Gpm = btuh/((EWT - LWT) * Specific Heat of Water * 60 * 8.33)

6800 btuh /((194-158) * 1 * 60 * 8.33) = .38 Gpm

40% of that would be about .15 Gpm

This flow rate will lower the leaving water temp to 103 deg F giving a 91 deg F Temp Difference (EWT-LWT).

The water temp entering when the outside air is 0 deg C is 141 Deg F - 91 deg F = 50 Deg F. Which is crap. Better get that flow restriction cleared or you'll crack your boiler.

Or are we to assume that the water system has been calibrated to give us the same loss due to reduced Delta T as the room will lose? Thus reducing the temperature difference. This would be common for an automatic outdoor reset system, but I don't think we have suffiecient data to determine the room temperature other than to say it should be the same as the design condition. The water temp changes not the room temp.