How Do You Calculate Transformer Losses from Open and Short Circuit Tests?

In summary, the conversation discusses the testing of a single phase transformer with a rating of 2200/220 V and 500kVA. The open circuit test yielded a voltage of 220V, current of 85A, and power of 1800W. The short circuit test resulted in a voltage of 95V, current of 227.3A, and power of 8200W. The equivalent resistance referred to the low voltage side was calculated to be 0.4179Ω, and the resistance of the low side winding was found to be 2.58Ω. The copper loss of the secondary winding during the open circuit test was determined to be -6400W, and the core loss
  • #1
alnywk
14
0
urgent: single phase transformer

Homework Statement



A 2200/220 V, 500kVA, 50Hz distribytion transformer has been tested by means of the open circuit. the test data obtained is as follow:
open circuit test: V(l)= 220V, I(l)= 85A, P(oc)= 1800W
short circuit test V(h)=95V, I(h)=227.3A P(sc)= 8.2kW



Homework Equations



1.equivalent resistance referred to the low voltage side (state all assumption)

2. resistance of the low side winding only

3.transformer copper loss of the secondary winding during the open circuit test

4. transformer core loss when rated voltage is applied

5. explain if it justified to use the power input during the open circuit test as core loss?



The Attempt at a Solution



please
 
Physics news on Phys.org
  • #2
check my answers below.1.equivalent resistance referred to the low voltage side (state all assumption)Assuming that the transformer is single phase, the equivalent resistance referred to the low voltage side can be calculated as follows: R(eq)= V(h)/I(h)= 95/227.3= 0.4179Ω2. resistance of the low side winding onlyR(l)= V(l)/I(l)= 220/85= 2.58Ω3.transformer copper loss of the secondary winding during the open circuit testP(cu,l)= P(oc)-P(sc)= 1800-8200= -6400W4. transformer core loss when rated voltage is appliedP(core)= P(sc)-P(cu,l)= 8200-(-6400)= 14600W5. explain if it justified to use the power input during the open circuit test as core loss?No, it is not justified to use the power input during the open circuit test as core loss as the open circuit test is conducted at no-load condition and hence the core loss is zero.
 
  • #3
provide more information on the specific questions or calculations needed to answer this prompt. it is important to have clear and specific information in order to provide an accurate and thorough response. Without this information, it is difficult to provide a meaningful answer. Please provide more details on the specific questions or calculations needed. Thank you.
 

1. What is a single phase transformer?

A single phase transformer is an electrical device that is used to transfer electrical energy between two or more circuits through the process of electromagnetic induction. It is commonly used to step up or step down the voltage level in a power system.

2. What are the components of a single phase transformer?

The main components of a single phase transformer include a primary winding, a secondary winding, a core made of laminated steel, and an insulating material. Some transformers may also have additional components such as cooling systems and tap changers.

3. What are the types of single phase transformers?

The two main types of single phase transformers are step-up transformers and step-down transformers. Step-up transformers increase the voltage level, while step-down transformers decrease the voltage level. Other types include autotransformers, isolation transformers, and variable transformers.

4. How does a single phase transformer work?

A single phase transformer works by utilizing the principle of electromagnetic induction. When an alternating current passes through the primary winding, it creates a changing magnetic field which induces a voltage in the secondary winding. This voltage is proportional to the number of turns in each winding and can be stepped up or down depending on the transformer's design.

5. What are the applications of single phase transformers?

Single phase transformers are widely used in various applications, including power distribution systems, electronic devices, lighting systems, and industrial machinery. They are also commonly used in household appliances such as refrigerators, air conditioners, and washing machines.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
7
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
6K
  • Engineering and Comp Sci Homework Help
Replies
20
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
6K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
10K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
  • Electrical Engineering
Replies
8
Views
2K
Back
Top