Can Two Control Signals Be Safely Connected to a Single Phase Contactor Coil?

In summary, two 120V control signals can be connected to a contactor coil and live at the same time, without causing a short or damaging any equipment.
  • #1
smoran22
2
0
If I have a contactor that I want to use with two separate control sources, on a site with a single phase power source, is it possible to connect two 120V control signals to the contactor coil, potentially live at the same time and connected to the same source, without causing a short, or damaging any equipment? The circuit is being designed to automatically turn on security lights at intervals set on a time clock, but with the addition of a manual override to turn on the lights as needed. I am not an electrician, but the work will be completed by a certified electrician once the planning for the building upgrades is complete. I'm just trying to understand how this would work. My understanding is that since the power is coming from the same breaker panel and the same power source, the two control voltages should always be in phase, eliminating the possibility of constructive and destructive interference. I would think that this setup would be considered a parallel arrangement? Meaning there would never be more than 120V supplied to the coil if both inputs were on, but the current available to the coil would be higher? Or would that supply too much current to the coil and cause problems? I'm just curious, I don't know how the electrical contractor will actually hook everything up when the time comes, but I have to admit I find this concept rather fascinating and I'd like to know a little more about it.
 
Engineering news on Phys.org
  • #2
If what you are suggesting is two switches in parallel sourced from the same exact breaker and connected to the same contactor terminal, then there is no issue.

If it is coming from a different breaker in the control panel, then NO! since it could come from different input leg (I guess you say it is single phase), and NO! you must not short the output of two breakers.
 
  • Like
Likes jim hardy and smoran22
  • #3
Thank you! I definitely learned from that! In the real world, is it likely an electrical contractor would do it this way, or would they likely do something entirely different? I know its hard to say because it depends on the contractor, but is there a simpler way to accomplish the same task?
 
  • #4
meBigGuy said:
NO! you must not short the output of two breakers.

not only mustn't you short them,

you mustn't mix their return wires either. What goes out through one breaker must return through THAT SAME breaker's neutral.
 
  • #5
Just tell the contractor to wire them from the same breaker. That is probably what he would do anyway if you told him nothing.
(assuming you are in a country with an enforced Electrical Code)
 
  • Like
Likes jim hardy
  • #6
Why does it have to be from two different sources? The same source can feed the timer AND the bypass switch - this is very common.
 
  • #7
If, indeed, you MUST use two sources from two different breakers, then you also need two contactors. The extra contactor, whose coil is powered by the second breaker through the bypass switch, switches power from the first breaker to the primary contactor. (or vice versa, the timer powers the second contactor)
 

1. What is a contactor and what is its purpose?

A contactor is an electrical device used to switch an electrical circuit on or off. It is typically used in high-power applications to control the flow of electricity to a motor or other load.

2. How do I wire a contactor?

The specific wiring process will vary depending on the type and model of the contactor, as well as the specific application. It is important to refer to the manufacturer's instructions or consult with a qualified electrician for proper wiring procedures.

3. Can a contactor be used with both AC and DC circuits?

Yes, there are contactors designed for use with both AC and DC circuits. However, it is important to ensure that the contactor is rated for the specific voltage and type of current being used.

4. What is the difference between a contactor and a relay?

A contactor is typically used for high-power applications, while a relay is used for lower-power circuits. Additionally, contactors are designed to switch larger currents and have a larger physical size compared to relays.

5. Can a contactor be used as a motor starter?

Yes, contactors are often used as motor starters in industrial and commercial applications. They provide a reliable and efficient way to control the power to a motor and protect it from overloads or other electrical issues.

Similar threads

  • Electrical Engineering
Replies
25
Views
2K
Replies
13
Views
2K
Replies
17
Views
686
  • Electrical Engineering
Replies
8
Views
731
Replies
3
Views
563
  • Electrical Engineering
Replies
11
Views
2K
  • Electrical Engineering
Replies
6
Views
13K
Replies
16
Views
2K
Replies
31
Views
2K
Replies
24
Views
4K
Back
Top