Cavitation in tubes of heat exchanger

In summary, the heat exchanger in the U-type has problems with erosion and corrosion near the beginning of the tubes. It is possible that cavitation is the problem. The exchanger is oversized, and the proper tube material may not have been selected for the fluid being handled.
  • #1
malkio
11
0
Hello!
In heat exchanger (U-type) I've problem with erosion/corrosion at beginning of tubes in heat exchanger,near tube-sheet where steam enters.i suspect cavitation is problem. on tubes there's a channel of erosion in the middle of tube where material is gone and tube is very thin in that channel,as tube continues channel is smaller and smaller,and finally there is normal cross-section of tube.medium in tube is 4bar steam used for heating methanol in shell side
anyone had experience with this? how to try solve this problem?
tnx
 
Engineering news on Phys.org
  • #2
Does your exchanger have an impingment plate installed at the inlet nozzle of the shellside? This keeps the steam from impacting the tubes at the shell inlet, causing caviation and errosion. If not currently installed, one could be added above the shell. This does not apply to your problem. I reread that steam is on the tubeside in your application.

How old is the exchanger?

Was the proper tube material selected for the fluid being handled?

Is the errossion inside the tubes or outside?
 
Last edited:
  • #3
Steam cavitation. Huh. Ya learn something new everyday. I immediately thought of impingement issues as well.
 
  • #4
Are you desuperheating your steam supply to the heat exchanger to get the maximum amount of work from it? If so, are you injecting the feedwater into the steam very close to the heat exchanger so that it does not have sufficient time to vaporize (erosion by impingement)? If you are indeed desuperheating with feedwater injection, and this is a new problem (it worked fine for a period of time without undue tube thinning) perhaps the feedwater injection nozzle has eroded to the point where it delivers a stream of feedwater instead of a fine spray, again leading to erosion from impingement. Good luck.
 
Last edited:
  • #5
Somone please enlighten me; I learned about cavitation as something that happens to liquids when pressure drops too much. The liquid briefly becomes a gas. How can steam cavitate if it's already a gas?
 
  • #6
LURCH said:
Somone please enlighten me; I learned about cavitation as something that happens to liquids when pressure drops too much. The liquid briefly becomes a gas. How can steam cavitate if it's already a gas?
I had never heard of it either. I'm curious myself. I did do a search and there is a website here: http://www.jlfiberservices.com/optima_online/refining/vol6/no_2/index.asp where there is a mention of a failure mode due to steam cavitation, but that's all there is on it. I can't find anything explaining the phenomena.
 
Last edited by a moderator:
  • #7
Heat exchanger is oversized (wrongsized)? You're doing all your heat transfer in "the channel," collapsing steam bubbles and getting the erosion?
 
  • #8
malkio hasn't been back to clarify, so we're left with little but speculation. Typically, these u-tube heat exchangers have a baffle running down the center and the product in the shell flows counter to the steam in the tubes. This let's the hottest steam contact tubes surrounded by the hottest product and the coolest, wettest steam contacts tubes surrounded by the coolest product, avoiding thermal shock and allowing heat transfer to occur gradually all along the length of the tubes.

I, too, am puzzled about the usage of the term steam cavitation, since that typically refers to the abrupt collapse of steam bubbles in a flow of liquid, like in a condensate line or perhaps a fuel injection system. Generally, when one thinks about mechanical erosion in a steam system, the culprit is "wet steam". That's why we superheat steam before passing it on to the steam distribution system and desuperheat it to near saturation just before introducing it to its loads.
 
  • #9
here i am,
i study my exchanger and cut some tubes,so here's little drawing of my case and picture of part of damaged tube.
As you see, damage is on the inner part of tubes where steam goes,damaged tubes are tubes on top of bunddle and upper part of tubes at aproximately in the middle of tube.
i first thought about cavitation but as you said cavitation happens in liquids so now I'm not sure i can explain mechanism which cause that erosion
as you see from temperatures my steam is not superheated ,it's probably some mixture condensate/steam
my theory is :mixture of steam/condens. came in tubes,condens. flows in lower part of tube and in upper part of tube is steam,in the middle of tube length (pointed at picture) where methanol (in shell) has lower temp. bubbles of steam begin to colapse (turn in condensate) and in that process devastate tube,maybe tubes on top of bunndle and upper parts of that tubes are most exposed to methanol temp. so that's where most of that transition steam bubbles-condensate hapenns.

i hope i make thing clear ,if i forget answer or mention something feel free to ask
i think one of solutions would be different material of tubes or superheating steam
any suggestions?
 

Attachments

  • exc.bmp
    27.8 KB · Views: 972
  • Picture 041.jpg
    Picture 041.jpg
    24.3 KB · Views: 951
  • #10
middle of tubes means middle of length of tubes (middle of exchanger)(drawing)
 
  • #11
If that eroded channel is on the top inside surface, you may very well be looking at a cavitation problem, as you suggested. That implies that the heat exchanger is doing almost all of its work (transferring the latent heat of vaporization) in that short little section of tubes near the product outlet pipe, and the remaining length of the tubes is carrying an almost solid plug flow of condensate. The tubes at the top of the bundle are exposed to the hottest flow of product, and the steam in them might not fully condense, carrying a mix of steam and condensate to the next chamber, where the steam bubbles collapse when they come into contact with the cooler tubes (surrounded by cooler product), resulting in erosion. That could be why you see the damage concentrated in the upper tubes just beyond the first baffle. I had assumed (wrongly) that you have a counter-flow heat exchanger that would minimize thermal shock, but from your drawing, the product flow is serpentine, and there is an area that is prone to thermal shock, right where the damage is concentrated. I am afraid that I don't see an obvious solution that doesn't involve re-engineering. Superheating the steam might just push the problem further downstream without solving it.

The most obvious solution would be to replace the heat exchanger with a vertically-mounted single-pass counter-flow unit. Steam enters the top, condensate exits the bottom, and product flows in at the bottom of the shell and exits from the top. This would minimize thermal shock and if cavitation did occur, it would not be confined to a small section of the tube interior, but would be evenly distributed.
 
Last edited:
  • #12
Just curious why this exchanger is setup with steam in the tubes and the Methanol in the shell?

Is the steam trap operating correctly, adequately sized and the proper type for the process to allow the condensate to be removed quickly enough? What kind of trap is it?
 
  • #13
turbo-1 tnx
very very helpful

artman
it's actually heater of methanol,why this setup i really don't know,maybe because of higher pressure of steam than methanol,hmm you make me thing,what if i switch this(steam -shell,methanol -tubes)? i don't know

i just working on checking steam traps along pipes ,but i think it's not main problem cause steam bubbles that condense along tubes devastate tubes not the condensate wihich is not being removed by steam traps,just thinking
 
  • #14
malkio said:
...it's actually heater of methanol,why this setup i really don't know,maybe because of higher pressure of steam than methanol,hmm you make me thing,what if i switch this(steam -shell,methanol -tubes)? i don't know...

Pressure could be the reason it is reversed from the norm, which would be to have the more corrosive material in the tubes.

malkio said:
i just working on checking steam traps along pipes ,but i think it's not main problem cause steam bubbles that condense along tubes devastate tubes not the condensate wihich is not being removed by steam traps,just thinking

turbo-1 said:
...and the remaining length of the tubes is carrying an almost solid plug flow of condensate...

If the trap does not remove condensate fast enough, this plug will grow larger backing up into the exchanger and reduce the capacity of the exchanger. If this plug moves suddenly, the pressure in the tube drops and the condensate at the steam end of the plug flashes to steam, causing hammering. The steam trap should be working at or near steam temperature, if condensate is allowed to form in the exchanger to that degree, the trap is probably operating considerably below steam temperature. Condensate allowed to cool below steam temperature forms carbonic acid, which also eats and pits piping.

Your entire exchanger should be filled with steam, with condensate only forming near the trap end. This is all a function of the trap.
 

Related to Cavitation in tubes of heat exchanger

1. What is cavitation in tubes of heat exchanger?

Cavitation in tubes of heat exchanger is the formation and collapse of vapor bubbles due to low pressure or high velocity in the fluid passing through the tubes. This can cause damage to the tubes and decrease the efficiency of the heat exchanger.

2. What causes cavitation in tubes of heat exchanger?

Cavitation in tubes of heat exchanger is caused by a combination of low pressure and high velocity in the fluid, leading to the formation of vapor bubbles. This can be due to obstructions or restrictions in the tubes, high fluid flow rates, or improper design of the heat exchanger.

3. What are the effects of cavitation in tubes of heat exchanger?

The effects of cavitation in tubes of heat exchanger can include erosion and damage to the tubes, reduced heat transfer efficiency, increased noise and vibration, and potentially even complete failure of the heat exchanger. It can also cause pressure drops, which can affect the overall system performance.

4. How can cavitation in tubes of heat exchanger be prevented?

Cavitation in tubes of heat exchanger can be prevented by ensuring proper design of the heat exchanger, including proper sizing and spacing of the tubes, as well as avoiding any obstructions or restrictions. Regular maintenance and cleaning of the heat exchanger can also help prevent cavitation. Additionally, controlling the fluid flow rate and pressure can help prevent cavitation from occurring.

5. How is cavitation in tubes of heat exchanger detected?

Cavitation in tubes of heat exchanger can be detected through various methods, including visual inspection for any signs of erosion or damage to the tubes, monitoring for changes in noise and vibration levels, and using specialized techniques such as ultrasonic testing. It is important to regularly inspect and monitor the heat exchanger to detect cavitation early and prevent any potential damage.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
Replies
18
Views
4K
Replies
7
Views
2K
  • Mechanical Engineering
Replies
3
Views
2K
Replies
12
Views
2K
Replies
2
Views
1K
  • Mechanical Engineering
Replies
34
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
2K
  • Materials and Chemical Engineering
Replies
4
Views
13K
Replies
1
Views
1K
Back
Top