Parallel Equipment Grounding Conductors, Short Circuit

In summary, the common interpretation of the National Electrical Code does not allow for the use of multiple smaller equipment grounding conductors in place of one larger one. There have been debates about the appropriateness of this standard, with considerations for fault current and inductive reactance. While it is allowed to use multiple smaller wires for ungrounded current carrying conductors, there is a holdout on equipment grounding conductors due to safety concerns. However, there are exceptions to this rule and discussions about the size of the equipment grounding conductor in relation to the ungrounded circuit conductors. Ultimately, the issue boils down to the division of fault current among parallel equipment grounding conductors and the requirement for all conductors to withstand the available fault current.
  • #1
Leyden
39
4
TL;DR Summary
Seeking information on parallel equipment grounding conductors fault characteristics.
I am seeking direction, information, resources and thoughts on the following subject. The common interpretation of the National Electrical Code does not allow you to use multiple smaller equipment grounding conductors in place of one larger one (except in a few cases such as a cable assembly, this thread is specifically dealing with single conductors in conduit). So, could anyone point me to any information, studies, etc. that would lead me to believe either this standard is appropriate or an overburden?

The issue I see at hand is fault current and the level at which a particular size of wire fuses/melts/fails. I think the major factor in the question is inductive reactance, some things that I think will play a large role in this are the proximity of the the equipment grounding conductor to the ungrounded conductors under fault and the proximity to grounded equipment foreign to the designed circuit (local metal objects), also carrying varying levels of fault current.

Some background information; You are allowed to use multiple smaller wires for ungrounded current carrying conductors. I believe the thought behind the holdout on equipment grounding conductors is because it is the safety conductor, so it is more safe for an ungrounded conductor to fail than an equipment grounding conductor.

Under the common interpretation of the standard, an equipment grounding conductor larger than the ungrounded circuit conductors could be required under certain circumstances, another less commonly accepted interpretation is that the ground does not have to be larger than the circuit conductors(in more common installations the ground is smaller than the circuit conductors).

It is already a related requirement for conductors to be able to withstand the available fault current but the basis of the question is the fault current dividing among the parallel equipment grounding conductors. The equipment grounding conductor size is based on the size of the overcurrent protection device, if you have parallel feeders say twelve sets of 600kcmill copper circuit conductors you may need a 800kcmill copper equipment grounding conductor in each of the twelve conduits.

Also, this is an old code requirement and has been contested through the years, the only legitimate argument I have seen to keep it is not an argument based on science that it should be required, but that to get rid of it requires clear scientific proof that it should not be required, that fault current will divide adequately and one parallel conductor will not bear too much of the brunt and fuse.Thank you
 
Last edited by a moderator:
Engineering news on Phys.org
  • #3
anorlunda said:
There's a pretty good discussion here https://iaeimagazine.org/magazine/2...ductors-for-parallel-conductor-installations/

including the criteria for exceptions to the rule.
Yes. A good discussion. I thought I'd add this image as a reference.

242937


image compliments of https://www.ecmweb.com/qa/stumped-code-installing-circuit-conductors-parallel-separate-raceways
 
  • Like
Likes jim hardy
  • #4
If I were forced to defend the status quo:
A connection failure in 1 (or more) power conductors in a multi-conductor feed may result in conductor overheating or system performance issues. That's bad, but probably won't kill anyone. A similar connection failure in safety grounds may prevent a breaker trip and/or allow a substantial voltage (to ground) to exist on things that are theoretically 'grounded.' Most important, the ground issue is nearly impossible to detect, unless you go looking for it - that usually happens as part of the accident investigation / lawsuit.
 
  • Like
Likes dlgoff and Asymptotic
  • #5
I agree, i believe i mentioned that in the original post. but there is already another requirement which both the equipment grounding conductor and the ungrounded conductors must both be able to survive the available fault current, so really if each of the grounds need to be that big then the ungrounded circuit conductors should be as well.

Technically I see a good argument that the ungrounded should be the bigger ones. For example, say an ungrounded circuit conductor of a parallel feeder installation somehow severs and the upstream side connects to grounded metal equipment , the entire available fault current is borne on the individual wire, while the current on the equipment grounds will divide(probably somewhat evenly, but I'm not sure enough about this part, this is the part the entire thread is about). just to try to illustrate the extreme, NEC allows you to parallel 1/0, so say the scenario has 10 parallel conduits of 1/0 ungrounded circuit conductors and 500Kcmil equipment grounding conductors in each conduit. a single 1/0 of a long run may posses enough impedance for a system like that to keep the protective device from opening, all while possibly introducing deadly voltage gradients in the area.
 

1. What are parallel equipment grounding conductors?

Parallel equipment grounding conductors are conductors that are installed in parallel with the main circuit conductors to provide a low resistance path for fault currents in the event of a short circuit.

2. Why are parallel equipment grounding conductors necessary?

Parallel equipment grounding conductors are necessary to protect electrical equipment and personnel from the dangers of short circuits. They help to quickly divert fault currents away from the equipment, preventing damage and potential electrocution.

3. How do parallel equipment grounding conductors work?

Parallel equipment grounding conductors work by providing a low resistance path for fault currents to travel through. This allows the fault current to bypass the equipment and flow back to the source, effectively clearing the fault and preventing damage.

4. How are parallel equipment grounding conductors installed?

Parallel equipment grounding conductors are typically installed in parallel with the main circuit conductors, meaning they run alongside each other. They are connected to the equipment being protected and to the grounding electrode system of the building.

5. What are the requirements for parallel equipment grounding conductors?

The National Electrical Code (NEC) sets specific requirements for parallel equipment grounding conductors, including size, material, and installation methods. These requirements ensure that the conductors are able to safely and effectively handle fault currents.

Similar threads

Replies
6
Views
1K
  • Electrical Engineering
Replies
9
Views
3K
  • Electrical Engineering
2
Replies
38
Views
5K
  • Electrical Engineering
Replies
2
Views
1K
Replies
13
Views
4K
Replies
16
Views
3K
  • Electrical Engineering
Replies
7
Views
2K
Replies
31
Views
2K
Replies
12
Views
7K
Replies
6
Views
5K
Back
Top