When designing a panel, it is imperative that you keep the components inside at a temperature which they can operate optimally at; allowing the air temperature to go above this limit can cause component failure and fire.
To assist with calculating the air flow required to keep the components below their maximum operating temperature, the IEC 60890 Heat Rise Standard was produced.
Within the calculations, there is a table to reference, where you get your 'c', 'f' and 'k' constants, which depending on the dimensions, effective cooling surface area of the panel, where the enclosure is installed, and if there is ventilation or not.
My question, is where are these constants derived from?
'c' is noted as the Temperature distribution factor
'f' is mathematically produced from the dimensions of the enclosure - (height^1.35)/(Width x Depth)
'k' is noted as the Enclosure constant
They seem like arbitrary numbers, but they are pretty specific:
For example, if you calculate your 'f' factor to be '2.8' and your panel was installed to be a single enclosure with all sides available for cooling, then your 'c' factor is '1.3185' and your 'k' factor is '0.121'.
I like to get into the nitty-gritty side of mathematics, so I'd love to know how these numbers are derived.
Thanks
To assist with calculating the air flow required to keep the components below their maximum operating temperature, the IEC 60890 Heat Rise Standard was produced.
Within the calculations, there is a table to reference, where you get your 'c', 'f' and 'k' constants, which depending on the dimensions, effective cooling surface area of the panel, where the enclosure is installed, and if there is ventilation or not.
My question, is where are these constants derived from?
'c' is noted as the Temperature distribution factor
'f' is mathematically produced from the dimensions of the enclosure - (height^1.35)/(Width x Depth)
'k' is noted as the Enclosure constant
They seem like arbitrary numbers, but they are pretty specific:
For example, if you calculate your 'f' factor to be '2.8' and your panel was installed to be a single enclosure with all sides available for cooling, then your 'c' factor is '1.3185' and your 'k' factor is '0.121'.
I like to get into the nitty-gritty side of mathematics, so I'd love to know how these numbers are derived.