Star/delta transformer - single phase fault on secondary

In summary: This is due to the presence of the zigzag earthing transformer, which provides a return path for the earth-fault current and prevents it from flowing through the primary side of the transformer.
  • #1
acw260
14
0

Homework Statement


A three-phase distribution transformer is configured as follows:
-primary side = star with solidly grounded neutral
-secondary side = delta, grounded via zigzag earthing transformer

A single phase-earth fault occurs on the secondary (delta) side of the circuit.

Homework Equations


Will current flow in the neutral connection on the primary side of the transformer (solidly grounded star)?

The Attempt at a Solution


I believe that the answer is 'no'.

If I understand correctly, the earth-fault current on the secondary (delta) side will flow back into the secondary side of the circuit via the zigzag earthing transformer and be evenly distributed between the phases. The primary (star) side of the transformer will therefore 'see' the fault as a balanced three-phase fault, with equal current flowing in each of the three legs of the delta windings. Therefore no current will flow on primary side neutral.

Is my understanding above correct? Any help would be much appreciated.
 
Physics news on Phys.org
  • #2


Yes, your understanding is correct. In this configuration, the earth-fault current will flow back into the secondary side of the circuit via the zigzag earthing transformer and will be evenly distributed between the phases. This means that no current will flow in the neutral connection on the primary side of the transformer. This is due to the fact that the neutral is solidly grounded, which means that it is connected directly to the ground and does not allow any current to flow through it.

The purpose of the zigzag earthing transformer in this configuration is to provide a return path for the earth-fault current, ensuring that it does not flow through the primary side of the transformer. This helps to protect the transformer from damage and also prevents any potential hazards to the system.

In summary, in this configuration, the primary side of the transformer will not see any current flowing in the neutral connection in the event of a single phase-earth fault on the secondary side.
 

1. What is a star/delta transformer?

A star/delta transformer is a type of transformer that is used to step down high voltage electricity to a lower voltage. It is named after the configuration of its windings, which resembles a star (Y) or a delta (Δ) shape.

2. How does a star/delta transformer work?

In a star/delta transformer, the primary winding is connected in a star configuration, and the secondary winding is connected in a delta configuration. This allows the transformer to convert three-phase power to single-phase power, or vice versa. It also provides a way to balance the load across the three phases.

3. What is a single phase fault on the secondary of a star/delta transformer?

A single phase fault on the secondary of a star/delta transformer refers to a situation where one of the three phases in the secondary winding becomes disconnected or grounded, causing an imbalance in the transformer's output. This can lead to damage to the transformer and other connected equipment.

4. What are the causes of a single phase fault on the secondary of a star/delta transformer?

The most common causes of a single phase fault on the secondary of a star/delta transformer are insulation breakdown, loose connections, and faulty equipment. These can be caused by factors such as aging, moisture, or improper installation.

5. How can a single phase fault on the secondary of a star/delta transformer be prevented?

To prevent a single phase fault on the secondary of a star/delta transformer, regular maintenance and testing should be performed to identify and address any potential issues. Proper installation and following safety protocols can also help prevent faults. In addition, using protective devices such as fuses and circuit breakers can limit the damage caused by a fault.

Similar threads

  • Electrical Engineering
Replies
8
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
2K
  • Electrical Engineering
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
8
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Electrical Engineering
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
6
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
Back
Top