In summary, the synchronizing module has 3 lamps that are connected to the 2 x 3 three phases. When the frequencies are mismatched, the lamps will flash. If the frequencies are matched and the phase is matched, the middle lamp will be switched off and the two outer lamps will shine exactly equally.
  • #1
askme
6
0
Hi I am Ken. Nice to meet you. I would like to get some info on this synchronizing module. It has a 3 phase lamp for synchronizing an alternator. Any knows what's the theory behind that flashing lamp? what if the lamp blink very fast or blinking slow? the reason is frequency is out of phase but i want to know in details what cause it to blink? Thanks.
 
Last edited by a moderator:
Engineering news on Phys.org
  • #2
askme said:
Any knows what's the theory behind that flashing lamp? what if the lamp blink very fast or blinking slow? the reason is frequency is out of phase but i want to know in details what cause it to blink?
I know about a module, that has 3 lamps ( an older analog version). These lamps are connected through a circuit to the 2 x 3 three phases. The circuit consist of resistors and capacitors in some arrangement ( don't remember how ). Of course the three lamps will flash when the frequecies are mismatched, but when the frequecies are matched and the phase is matched, the middle lamp will be switched of, and the two outer lamps will shine exactly equally.

If your module acts different, I think that it could have been made, based on a μ-processor. Then there is a lot of methods, how to program the processor. The simplest way would be to measure when the 2 x 3 phases cross zero. Then to calculate/determine how your lamp should react ( the HMI, Human-Machine-Interface ).
 
  • #3
Simplest form is simply a light between the two machines.

you can use three lamps, one per phase if you wish but one will do the job

synchronization+of+alternator.png


It should be obvious that when the machines are in phase there's no voltage across the lamps and they all 3 go out,
so it's safe to close the switch when the lamps are out

whenever the machines are not in phase there will be voltage across the lamps
e.g.
at any instant the voltage across a lamp will be the difference (vertical distance) between red and blue voltages
220px-Phase_shift.svg.png

and as phase shifts between 0 and 360 degrees, that voltage difference will grow from zero to twice peak than back to zero

so your synch module must either :
use lamps rated for twice voltage,
or do what we did in the power plant - two lamps in series.

Used to be in Great Britain they preferred to wire their lamps through transformers and swap phase so that the proper time to close the switch was maximum brightness instead of minimum. Sophie might know if that's still the practice.

The lamps also tell you if there's a voltage mismatch - the they'll never quite go out.
 
  • #4
jim hardy said:
when the machines are in phase there's no voltage across the lamps and they all 3 go out
I think it is very difficult to see if the lamps have gone completely out ( easier to see if two lamps have the same brightness ).

Also it's difficult to estimate maximum brightness.
 
  • #5
Hesch said:
I think it is very difficult to see if the lamps have gone completely out ( easier to see if two lamps have the same brightness ).

Also it's difficult to estimate maximum brightness.

The skill lies in timing the peaks (of brightness or darkness, whichever you prefer)
you want the unloaded machine to be going very slightly faster than the bus to which you are about to connect it
so that when breaker closes, it provides power rather than absorbing it
because big generators have protective relays to disconnect them when they're "motoring"
and it's really embarassing to synchronize successfully only to have the automatic protection equipment disconnect you a few seconds later

so the operator adjusts governor valves to make the lights cycle through their dark-dim-bright-dim-dark cycle once every several seconds
with his machine going just a few RPM faster than synchronous, maybe 3005 or 3610 RPM
When he feels he's "Got the rhythm" he'll close the switch at the right moment.

It's easier with a synchroscope, which is just a rotating phase angle meter
this one's showing 90 degrees out of phase
proper time to close is - needle rotating slowly clockwise and it reaches straight up
upload_2015-8-6_15-19-40.jpeg

we had our lamps immediately above the synchroscope
 
  • #6
I've tried to google circuit+synchronize+alternator, but cannot find the circuit mentioned in #2.

But I remember we had a question at some examination, how to design/calculate resistors and capacitors.

That was easy. But since then, I've have become much older, so now it's not easy. :sorry:

I'll think about it, then I will dream about it, ( must remember to have a pencil and sheet of paper ready, awaking from the dream in the middle of the night ).
 
Last edited:
  • #7
Is this it ?
Looks like just lights...
upload_2015-8-6_16-18-34.png
 
  • #8
askme said:
Hi I am Ken. Nice to meet you. I would like to get some info on this synchronizing module. It has a 3 phase lamp for synchronizing an alternator. Any knows what's the theory behind that flashing lamp? what if the lamp blink very fast or blinking slow? the reason is frequency is out of phase but i want to know in details what cause it to blink? Thanks.

This PDF appears to have some related information:

https://www.google.com/url?sa=i&rct=j&q=&esrc=s&source=images&cd=&cad=rja&uact=8&ved=0CAkQ5TVqFQoTCMuE9_HAlccCFU2ZiAodoa4Dnw&url=https://www.labvolt.com/downloads/datasheet_98-8013-0_en_120V_60Hz.pdf&ei=1t_DVcvBGs2yogSh3Y74CQ&bvm=bv.99804247,d.cGU&psig=AFQjCNH-KZ-YHcA_WbMWE4zXDq7Ifg2KYQ&ust=1438986578772572

Use the search feature to look for the instances of 8110-20 in the PDF file -- there are several with pictures.

:smile:
 
  • #9
jim hardy said:
It should be obvious that when the machines are in phase there's no voltage across the lamps and they all 3 go out,
so it's safe to close the switch when the lamps are out

whenever the machines are not in phase there will be voltage across the lamps
e.g.
at any instant the voltage across a lamp will be the difference (vertical distance) between red and blue voltages
d.wikimedia.org%2Fwikipedia%2Fcommons%2Fthumb%2F5%2F55%2FPhase_shift.svg%2F220px-Phase_shift.svg.png

and as phase shifts between 0 and 360 degrees, that voltage difference will grow from zero to twice peak than back to zero

so your synch module must either :
use lamps rated for twice voltage,
or do what we did in the power plant - two lamps in series.

Used to be in Great Britain they preferred to wire their lamps through transformers and swap phase so that the proper time to close the switch was maximum brightness instead of minimum. Sophie might know if that's still the practice.

The lamps also tell you if there's a voltage mismatch - the they'll never quite go out.
Thank you so much. Much appreciated
 
  • #10
Hesch said:
I know about a module, that has 3 lamps ( an older analog version). These lamps are connected through a circuit to the 2 x 3 three phases. The circuit consist of resistors and capacitors in some arrangement ( don't remember how ). Of course the three lamps will flash when the frequecies are mismatched, but when the frequecies are matched and the phase is matched, the middle lamp will be switched of, and the two outer lamps will shine exactly equally.

If your module acts different, I think that it could have been made, based on a μ-processor. Then there is a lot of methods, how to program the processor. The simplest way would be to measure when the 2 x 3 phases cross zero. Then to calculate/determine how your lamp should react ( the HMI, Human-Machine-Interface ).

Thank you for the info :D. But do you know what actually caused the flashing lamp to blink fast and slow? The reason behind it.
 
  • #11
jim hardy said:
Is this it ?
Looks like just lights...
View attachment 86975
yes this the one I am using. Because I am analyzing on an alternator synchronization. module needed is the synchronous motor/generator and DC motor/generator. So now I just to get the theory behind that flashing 3-phase lamps.
 
  • #12
  • #13
askme said:
So now I just to get the theory behind that flashing 3-phase lamps.

jim hardy said:
whenever the machines are not in phase there will be voltage across the lamps
e.g.
at any instant the voltage across a lamp will be the difference (vertical distance) between red and blue voltages
d.wikimedia.org%2Fwikipedia%2Fcommons%2Fthumb%2F5%2F55%2FPhase_shift.svg%2F220px-Phase_shift.svg.png

and as phase shifts between 0 and 360 degrees, that voltage difference will grow from zero to twice peak than back to zero
The lamps are connected between the two generators, that is between the ed and blue sinewaves
one lamp(or pair of lamps) for each of three phases
when the voltage is high the lamps are bright indicating the two sine waves are not aligned vertically, ie in phase
when the sine wavs come into phase , ie vertically aligned, the voltage across the lamps becomes zero so the lamps extinguish
that's the time to close your breaker because zero volts means not much current will flow.
Closing the breaker when voltages are out of phase causes high current and largetorques, it's a violent manuever.

interesting video demonstration here with stroboscope
 
  • #14
jim hardy said:
The lamps are connected between the two generators, that is between the ed and blue sinewaves
one lamp(or pair of lamps) for each of three phases
when the voltage is high the lamps are bright indicating the two sine waves are not aligned vertically, ie in phase
when the sine wavs come into phase , ie vertically aligned, the voltage across the lamps becomes zero so the lamps extinguish
that's the time to close your breaker because zero volts means not much current will flow.
Closing the breaker when voltages are out of phase causes high current and largetorques, it's a violent manuever.

interesting video demonstration here with stroboscope
Thank you so much Jim hardy. This is the part that I wanted. introduction and sync lamps. :smile::smile:
 

1. What is the purpose of the Synchronizing module lab volt Model 8110-20?

The Synchronizing module lab volt Model 8110-20 is used to synchronize multiple generators and ensure that they are operating in parallel with each other. It is commonly used in power generation systems to maintain a stable and reliable power output.

2. How does the Synchronizing module lab volt Model 8110-20 work?

The Synchronizing module lab volt Model 8110-20 uses electronic circuitry to compare the frequency and voltage of multiple generators and make adjustments to ensure that they are synchronized. It also has built-in protection mechanisms to prevent any potential damage to the generators.

3. Can the Synchronizing module lab volt Model 8110-20 be used with any type of generator?

Yes, the Synchronizing module lab volt Model 8110-20 is designed to work with a variety of generators, including diesel, gas, and steam turbines. It can also be used with both single and three-phase generators.

4. Is the Synchronizing module lab volt Model 8110-20 easy to install?

Yes, the Synchronizing module lab volt Model 8110-20 comes with detailed instructions and can be easily installed by following the step-by-step guide. However, it is recommended to have a professional electrician perform the installation to ensure proper and safe operation.

5. Does the Synchronizing module lab volt Model 8110-20 require regular maintenance?

Yes, like any electronic equipment, the Synchronizing module lab volt Model 8110-20 requires regular maintenance to ensure optimal performance. This includes checking and calibrating the settings, as well as conducting routine inspections for any potential issues.

Similar threads

Replies
1
Views
971
Replies
2
Views
1K
Replies
3
Views
565
  • Electrical Engineering
Replies
8
Views
11K
Replies
9
Views
5K
Replies
4
Views
4K
  • Astronomy and Astrophysics
Replies
3
Views
1K
Replies
7
Views
25K
  • Electrical Engineering
Replies
1
Views
2K
Replies
4
Views
3K
Back
Top