Neutral conductor.

Where can I find information about strange installations sharing the neutral conductor between two different installations ?

Best Regards
 
Engineering news on Phys.org
  • #2
I don't know what you mean by "Strange installations" but here are the http://ecmweb.com/search/results/shared%20neutral of the Electrical Construction & Maintenance site whom provides very good information for all sorts of electrical situations.
 
  • #3
Running to see
Best Regards
 
  • #4
Diagram it... #1 activity
 
  • #5
Windadct said:
Diagram it... #1 activity
Nice idea. I haved no much idea of possible combinations diagrams. But I will try in my next post.
Best Regards
 
  • #6
When draw I fell is not possible.
I assumed that are two differents installations.
Each one with a electricity meter above.
If these electricity meters are independent or not join above we don't close the circuit...

Circuit 1
electrical meter 1
Phase 1
Neutral 1

Circuit 2
electrical meter 2
Phase 2
Neutral 2

If we use Phase 1 and Neutral 2 I think nothing happen.

Except, perhaps, if the electrical meters are joined above.

My confusion began with the shared neutral in a triphasic circuit. But this is completely different to what i was thinking...

The circuit is not closed and nothing happen.

Best Regards
 
  • #7
Pifico said:
Neutral conductor.

Where can I find information about strange installations sharing the neutral conductor between two different installations ?

Best Regards

Illegal by most code books these days for loads, but they do actually work and were used many years in the past. Actually, they are used quite often but in a different way...

You can obviously google it, but you can share a neutral between two loads in a single phase 240/120 house panel board for example.
Meaning you can you one single romex and feed two loads like let's say two electrical outlets that both have their own breaker switch and sharing the neurtal from one romex. One wire of the romex (say the black) will hook in a 20 amp single pole breaker, then the other wire of the romex (say the white) will get wired into the 20 amp single pole breaker right beneath it...therefore they are 180 degrees out of phase, or you can say that each load is off of a different bus bar in the panel.

The reason you can theoretically do this is that the currents are litterally out of phase, the sin waves are flipped. Therefore the current through the neutral never exceeds 20 amps do to the "crossing out" effect.

You can see how the black and white wire is confusing. 30 years down the road the next guy comes in and does some rewiring. He doesn't know it is a edison circuit and re-wires it to a new load...except now he has line to line voltage...or 240 volts. Bad things happen when you hook 120 volt devices to 240 volt power supplies. For example, a light will burst, a vacuum cleaner will start on fire, a television will just plain fry...etc.

Actually, come to think of it, the wiring coming from the transformer into your home panel is a edison circuit, but a legal one. They share the neutral, but the bus bars are 180 degrees out of phase. The source is a center tapped secondary from the nearest transformer. The wiring is ussually red and black with the neutral being white.
 
Last edited:
  • #8
If i understand well you can use a shared neutral in a triphasic installation. The same neutral for triphasic outlets and for the monophasic outlets
 
  • #9
Pifico said:
If i understand well you can use a shared neutral in a triphasic installation. The same neutral for triphasic outlets and for the monophasic outlets

Yes, three phase can share a neutral as well if you are looking for 480/277 Volt for example, or 208/120 as another example.

But typically, motors are powered by three phase with no neutral, just a 3 conductor plus ground if you will.
 
  • #10
An electric oven also could have a somewhat simliar situation with single phase. It has line to line voltage with a neutral. 240 volt for the oven and 120 volts for the controls.

The difference is that the breaker in the panel is 2 pole instead of the two separate single breakers mentioned above.
The 2 pole breaker will be connected together mechanically.
 
  • #11
Understood.
Best Regards
In a car under DC is similar. the neutral is the ground.
 

Related to Understanding Neutral Conductor Sharing in Multiple Installations - Expert Guide

What is a Neutral Conductor?

A Neutral Conductor is a type of electrical conductor that is used in three-phase power systems to help balance the load and return current to the source. It is typically connected to the center tap of a transformer and has a voltage potential of zero, acting as a reference point for the other conductors.

Why is a Neutral Conductor necessary?

A Neutral Conductor is necessary because it helps to prevent overloading in the other conductors by providing a return path for the unbalanced current. Without a Neutral Conductor, the other conductors would have to carry all of the current, which could lead to overheating and potential damage to the electrical system.

What is the difference between a Neutral Conductor and a Ground Conductor?

A Neutral Conductor and a Ground Conductor serve different purposes. A Neutral Conductor is used to balance the load and return current to the source, while a Ground Conductor is used to provide a safe path for electrical current to flow to the ground in the event of a fault or surge. They are both important components of an electrical system, but they have distinct functions.

Can a Neutral Conductor carry current?

Yes, a Neutral Conductor can carry current, but it is typically designed to carry only the unbalanced current in a three-phase power system. This means that in a balanced system, the Neutral Conductor should have little to no current flowing through it. However, in the event of an imbalance, the Neutral Conductor may carry a significant amount of current.

What happens if a Neutral Conductor is damaged or disconnected?

If a Neutral Conductor is damaged or disconnected, it can lead to an imbalance in the electrical system, which can cause overloading and potential damage. It can also create a safety hazard as the voltage potential on the other conductors may become unstable. It is important to regularly inspect and maintain the Neutral Conductor to ensure it is functioning properly.

Similar threads

Replies
28
Views
1K
  • Electrical Engineering
Replies
17
Views
2K
  • Electrical Engineering
Replies
32
Views
2K
Replies
25
Views
2K
Replies
10
Views
1K
  • Electrical Engineering
Replies
4
Views
1K
Replies
19
Views
678
  • Electrical Engineering
Replies
27
Views
4K
  • Electrical Engineering
Replies
8
Views
2K
  • Electrical Engineering
Replies
6
Views
2K
Back
Top