Recent content by Manoj Sahu

  1. Manoj Sahu

    Why do Current Transformer cores have different knee point voltages?

    Exactly. It's installed in a 66kV Gas Insulated Substation
  2. Manoj Sahu

    Why do Current Transformer cores have different knee point voltages?

    It has 4 core marked as 1S1-1S2-1S3 400-300/1A 2S1-2S2 3S1-3S2 4S1-4S2
  3. Manoj Sahu

    Why do Current Transformer cores have different knee point voltages?

    As you said metering core needs to be accurate all the time and protection core accuracy must be at least known or 10- 20 nominal current, is this the reason protection core is having larger saturation point. I have a CT in which there are 4 core. The first core is used for metering whereas the...
  4. Manoj Sahu

    Why do Current Transformer cores have different knee point voltages?

    Yes. Exactly. Voltage on y -axis and Current on x -axis. You have marked at the right place. The result was as follows Knee point voltage -804V Current - 5.508 mA
  5. Manoj Sahu

    Why do Current Transformer cores have different knee point voltages?

    While doing the knee point test, I injected voltage upto 1500 V in a current transformer having knee point voltage 750V @ 30mA. The test was performed using Omicron's CPC 100 and it also had option to demagnetize.
  6. Manoj Sahu

    Why do Current Transformer cores have different knee point voltages?

    Thanks Jim I meant calculated/decided by the designer. If a current transformer is saturated, does it act like permanent magnet.
  7. Manoj Sahu

    Why do Current Transformer cores have different knee point voltages?

    I have to test a Current transformer. I read knee point is a point at which 10% increase in voltage leads to 50% increase in current. As there are different classes of current transformer (cores), how it is decided what/how much will be the knee point voltage of that core.
  8. Manoj Sahu

    Why do we use a Contact Resistance Measurement test?

    I don't exactly remember. Suppose, it is 13. How will we calculate?
  9. Manoj Sahu

    Why do we use a Contact Resistance Measurement test?

    I performed this test on Siemens 33kV GIS 8DB 10 panel. The test results were around 210micro ohm whereas the ideal values were 173micro ohm. I asked my Seniors , how come they calculated the ideal value of 173 micro ohm. They told me that it depends on number of contacts and can be easily...
  10. Manoj Sahu

    Why do we use a Contact Resistance Measurement test?

    I was wondering about contact resistance measurment test. Why do we take such test?
  11. Manoj Sahu

    Difference between a circuit breaker and a load break switch?

    This is very helpful. Can you please suggest me few sources or references to read more about this topic?
  12. Manoj Sahu

    Difference between a circuit breaker and a load break switch?

    Thank you for replying. Practically, I have observed few things. When the circuit breaker is ON, the load break switch can be turned ON or OFF but the Earth switch cannot be turned ON. Similarly, when Earth switch and breaker is ON, load break switch cannot be turned ON
Back
Top