The discussion centers on the unexpected tripping of an RCD (Residual Current Device) when an Earth leakage fault is induced downstream of a UPS (Uninterruptible Power Supply) in normal mode. Participants explore the possibility that the UPS may not be true dual conversion, as it seems to allow leakage current to affect the RCD. The conversation also touches on the behavior of the RCD in bypass mode and the impact of common-mode load changes due to transformer capacitance. Experimentation with different fault conditions, including resistor faults, is suggested to better understand the RCD's sensitivity. Overall, the interaction highlights the complexities of UPS design and its interaction with protective devices like RCDs.
qbnchopper
Messages
3
Reaction score
0
Gents, Ladies,

I have a design where I have:

AC -> RCD -> UPS (dual conversion apparently) -> PowerStrip -> Equipment

If I induce an Earth leakage fault downstream of the UPS (i.e. at the powerstrip), the RCD upstream of the UPS trips.

The UPS is in the "normal" not bypass state, and the UPS is supposedly dual conversion.

I cannot understand how this can happen unless the UPS is not true dual conversion !

Can someone confirm or debunk my understanding here please ?

Q
 
Engineering news on Phys.org
Another name for the RCD is GFCI, BTW. Does the GFCI trip if the UPS is in bypass mode too? I agree that if it really has switching power supply transformer isolation between the AC Mains with the GFCI, and the load where you introduce the ground fault, that the GFCI should not see anything different, other than a slight change in its AC load (no common-mode load change).

On second thought, it might see a common-mode load change because of the winding-to-winding capacitance of the switching transformer. Does it only trip the GFCI if you introduce a hard fault to ground (like with a wire)? What if you use a 10kOhm resistor instead? Try some resistor faults right at the GFCI to see where its sensitivity threshold is, and then do the same downstream of the UPS. It may just be the capacitive common-mode transient from a hard wire fault downstream of the UPS that is tripping the GFCI.
 
Last edited:
Berkeman,

Thanks for your reply ! I new that the RCD was called something else - but couldn't remember ...

Being an Aussie - RCD = Aussie; GFCI = American ? :-)

In bypass mode, the RCD/GFCI trips as expected.

In normal mode, the RCD/GFCI trips (not really as expected - but noting your second though!)

I am using a tool to induce the Earth leakage fault - it allows me to change the mA-erage to see how quickly an RCD responds. I came across this situation when I was testing to see if the UPS had anything in it to cope with a Earth leakage fault (i.e an experiment) ...
Anyway, I'll look at the tool and also try as you suggest ...

Thanks !
 
Glad to help, qbnchopper, and welcome to the PF. It's a great place.

I'd really be interested in the results of your experiments. Your initial test results are a bit non-intuitive for me as well.
 
The UPS loops the ground circuit thru to the UPS outlet.
I'm not entirely certain, but I think they also loop the neutral line thru.
If so, then at some point in a normal mains circuit the neutral and ground lines have a common bond.
Then a leakage current from the UPS hot to ground will loop back thru the neutral to complete the circuit. The unbalanced current in the RCD (GFCI) neutral will cause the breaker to trip.
 
Notime,

Thanks and Interesting ... in my case the Earth and neutral are not bonded ... however, on another problem that I am working that is related, earth/neutral are bonded upstream of the ups ... have to have a think about this ...

Q
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...

Similar threads

Replies
4
Views
8K
Back
Top