An AC source of 200 V RMS supplies 600 W of active power and 800 VAR of reactive power, leading to a calculated rms current of 3.75 A, contrary to the incorrect value of 5 A initially derived. The user attempted to calculate current using the formula involving the sum of squared powers but misapplied the concept. A suggestion was made to consider a resistive and reactive load in series, leading to the correct calculation of impedance. The discussion also touched on the confusion surrounding the square root of 3 factor, which is relevant in three-phase systems but not applicable here. Ultimately, the correct approach clarified the misunderstanding and confirmed the accurate current value.
dhruv.tara
Messages
45
Reaction score
0
Now this is not a homework question, just a practise question and my answer doesn't match.

An AC source of 200 V rms supplies active power of 600 W and reactive power of 800 VAR. The rms current drawn from the source is ? (the answer is 3.75 while mine is 5)

I did was squared and added the powers to get V^2*I^2, plugged in the value of V and got I as 5... Any help?
 
Engineering news on Phys.org
I like your answer.

Try it with 24 ohms resistive and 32 ohms reactive in series.
I squared R:
5 * 5 * 24 = 600 watts
I squared X
5 * 5 * 32 = 800 VAR

resultant of r + x:
SQ rt of (24 * 24 + 32 * 32) = 40 ohms
200 V / 40 ohms = 5 amps
 
Last edited:
p=sqrt(3)*V*I*p.f
 
from where did that sqrt(3) factor come into? I have seen this factor before, but as far as I remember that was in 3 phase systems... And I am not dealing with such problem yet I think...
 
sorry, my mistake, you're right dump the sqrt(3).
 
hmm okiess... thanks all
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top