Arcing - What affects size of arc when switch is opened?

  • Thread starter Thread starter Crazyhorse2882
  • Start date Start date
  • Tags Tags
    Arc Switch
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
5 replies · 2K views
Crazyhorse2882
Messages
20
Reaction score
0
When an electrical circuit is opened or closed there is an arc between the terminals/buss that the switch or breaker is connecting or disconnecting and the arc is greater depending on the amount of voltage. My question is, is the arc greater when there is a resistance/load on the circuit? I'm guessing yes, but what is the effect and how could you calculate it?
 
Engineering news on Phys.org
You have to consider the whole circuit to determine that.
In general, inductances (especially coils), large switching voltages and large currents will increase the amount of arcing you get.
 
Crazyhorse2882 said:
... is the arc greater when there is a resistance/load on the circuit? ...

Without a resistance/load, you wouldn't have a circuit in the first place, and therefore wouldn't have an arc at all.
 
So then if a main breaker was closed outside of a building feeding equipment inside the building but their individual circuits were open then there would be no arc as that breaker closed? There would be voltage but no current and my understanding is that it will arc
 
Crazyhorse2882 said:
So then if a main breaker was closed outside of a building feeding equipment inside the building but their individual circuits were open then there would be no arc as that breaker closed?
That is correct.
There would be voltage but no current and my understanding is that it will arc
No, it will not arc.
 
To emphasize this point - for medium voltage switches - there are two general classes "no load disconnect" and "load disconnect" - The no load types are ideally interlocked ( often literally with locks and keys - ref Kirk Key) - with the load side circuit breaker. The Load side circuit breaker must be open - to get the key that allows the line side "no load" switch to be operated ( opened or closed).
TO feed a transformer a MV switch used on the primary is technically a load break switch (it will have an arc chute & arcing contacts- separate form the main contacts) , but only rated to interrupt the magnetizing current of the transformer it feeds - so you still see the interlocking scheme.