deckart
- 106
- 4
jim hardy said:again you're skimpy on detail.Are you locked into a single machine?
Does hydraulic imply low RPM ?
An alternator would relieve the need for an inverter, simplifying maintenance.
Searching for "low RPM alternator"
turns up whoever's bribed google
here's a 10 kw 50 RPM permanent magnet three phase unit
http://www.xindaenergy.com/10Kw-50r...Generator-for-vertical-wind-turbine-p205.html
here's an old line manufacturer that makes generators for industry
http://www.emersonindustrial.com/en...ernators/power-alternators/Pages/default.aspx
number of poles you'd want is
(3600/RPM of your torque supply ) X 2 and it has to be an even integer
ie
3600 rpm = 2 pole
1800 rpm = 4 pole
900 rpm= 8 pole
720 rpm = 10 pole
I used a 150 kw Kato machine for our simulator, found it well made and reliable
how 'bout that - Emerson bought them.
http://www.emersonindustrial.com/en...s/katoengineering/Pages/Kato-Engineering.aspx
good luckIf this is a "Red Green" project, a dozen truck alternators could make your 800 amps DC
View attachment 93706
check your PBS listings...
Jim, help me out on the details that are needed. I know I'm not asking the question correctly. I'm not sure how to ask it other than I want to convert up to 50 mechanical horsepower to grid ready 37.3 kW. This is a bridge I don't know how to build. What I don't understand is the kind of loading I will need to design to. When working with mechanical rotary applications I'm used to designing to loads and RPM/velocities that are predefined.
<101 electrical theory
What I've come to believe is that an electric motor is a generator when rotated in the opposite direction. So my vastly limited electrical brain thinks I should design to a 50HP, 1750 RPM, "off-the-shelf" electric motor and have the "sparky's" wire it up and make it work. That gives me a fixed torque (assuming there is a fixed load?) and from there a fixed hydraulic motor displacement. I could design the hydraulics to do that but it would be in intervals as the hydraulic energy was accumulated and then delivered to the hydraulic motor. So far, I've read that wind generators do this but don't store any of the energy when the wind velocities aren't there. Shutting down when the wind velocities where too low and then coming on line when they pick up. But they are able to work with varying wind velocities/rotor rpm after a minimum is reached.
So, a couple of my questions are, "will there be a constant load?", and "what is the RPM range?". I'm still confused on where the load comes from. In order to get a load from the grid, don't we need a higher voltage? This is where I'm in the weeds.
The hydraulic associations I have are:
voltage = pressure
current = flow
In order to get flow you need a pressure differential.
(What's required to get the AC sine waves synced up to the grid is a whole nuther topic.)
I see that my inquiries are all over the place, and that's why I'm here. I really appreciate your input.