Caculation of line current on a 3 phases unbalanced delta

Click For Summary
SUMMARY

The discussion centers on calculating line currents (I1, I2, I3) in a three-phase unbalanced delta system with a 220V AC supply and a 3300W pure resistance load. Participants utilized Kirchhoff's Current Law (KCL) and complex number calculations to derive the currents, ultimately confirming that I1 = 15A, I2 = 15A, and I3 = 26A. The conversation also highlighted the importance of understanding phase relationships and the distinction between phase and line voltages in different regional contexts, particularly between the US and Europe.

PREREQUISITES
  • Understanding of three-phase electrical systems
  • Familiarity with Kirchhoff's Current Law (KCL)
  • Knowledge of complex number calculations in electrical engineering
  • Awareness of phase versus line voltage terminology
NEXT STEPS
  • Study the application of Kirchhoff's Current Law in three-phase systems
  • Learn about complex number representation in AC circuit analysis
  • Explore the differences in electrical terminology and standards between the US and Europe
  • Investigate the implications of unbalanced loads in three-phase systems
USEFUL FOR

Electrical engineers, students studying power systems, and professionals involved in three-phase circuit design and analysis will benefit from this discussion.

JumpZero
Messages
2
Reaction score
0
Hello,
I cannot find back from school, the formula to use:
A 3 phases 220Vac system, no neutral, 3300W of pure resistance load between L2 and L3, the same load between L1 and L3, nothing between L1 and L2.
What will be I1, I2, I3 the current in the 3 lines of the network?

Thanks in advance
--
Jmp0
 
Engineering news on Phys.org
Assume V1 = 220 / 0, V2 = 220 / 120, V3 = 220 / 240.

Calculate I23 and I13. (I23 is current from L2 to L3 ).

I2 = I23, I3 = -I23 - I13 (KCL)

I1 + I2 + I3 = 0 (KCL)

Calculate with complex numbers all the way.
 
Last edited:
I agree with Hesch except the voltages are V12=220>0,V23=220>-120,V31=220>-240[or +120] and since the load it is declared as “pure resistance” [cos(fi)=1] the currents will be:

I12=0;I23=3300/220*[(COS(-120)+SIN(-120)j];I31=3300/220*[(COS(+120)+SIN(+120)j]
upload_2015-4-28_7-52-7.png


Considering all currents “entering” position:

I1=I13=-I31=-15*[(COS(+120)+SIN(+120)j] =7.5-12.99j;I2=I23=-7.5-12.99j;I3=-I1-I2=2*12.99j=25.98j.Remark: the imaginary part of the current here it does not mean reactive part. The reactive part will be proportional with the sinus of angle between current and supplied voltage[fi] which remains 0 [in this case].

One could calculate also-following Hesch logic-using a trigonometric circle and use X and Y coordinates instead of complex number. The circle radius is equal to I=P/V=3300/220=15 [A]. Then:
upload_2015-4-28_7-52-45.png


I23X=-15*SIN(30)=-7.5[A]; I23Y=-15*SIN(60)=-12.99 [A]; I31X=-15*SIN(30)=-7.5 [A]; I31Y=+15*SIN(60)=12.99[A].

I1=I13=-I31 =7.5X-12.99Y;I2=I23=-7.5X-12.99Y;I3=-I1-I2=-(I1+I2)=2*12.99Y=25.98[A].
 
Hello,

Thanks for your answers. This is correct. I found it also (with help) with another method and result are the same:
I1=15A I2=15A I3=26A
This method:
Phase currents = I=P/E, = O amps for L1-L2 (ab) 3300/220 = 15A for L2-L3 (bc) & 15A for L3-L1 (ac)
Line currents =
L1 =√(ab²+ac²)+(ab x ac),
L2 =√(ab²+bc²)+(ab x bc),
L3 =√(ac²+bc²)+(ac x bc)

Thanks everybudy
--
Jmp0
 
It is a very interesting formulas. The complete one it is as following:

L3 =√(ac²+bc²)-2x(ac x bc)xcos(angle)

and for "angle" between ac and bc vectors[let's say "phasors"] of 120o turn it in:

L3 =√(ac²+bc²)+(ac x bc) [as you said]

As you can see for any other angle an error occurs.
 
Hesch said:
Assume V1 = 220 / 0, V2 = 220 / 120, V3 = 220 / 240.
(note my underline).
Babadag said:
I agree with Hesch except the voltages are V12=220>0
JumpZero said:
A 3 phases 220Vac system

Well, in Denmark (Europe) we operate with a phase-system (voltages and currents are as per phase) and a main-system (voltages and currents are phase to phase). So when I read "3 phases 220V", I regard 220V per phase to be meant ( V12 = 220V*√3 )?? In Europa we would write this: A 3×380V system.

I don't want to introduce a discussion about these different terms in US/EU, this is meaningless. I'm just trying to clarify the reason to some confusion
 
Last edited:

Similar threads

Replies
35
Views
5K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 26 ·
Replies
26
Views
3K
Replies
2
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 77 ·
3
Replies
77
Views
8K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 15 ·
Replies
15
Views
6K
  • · Replies 15 ·
Replies
15
Views
6K
  • · Replies 20 ·
Replies
20
Views
3K