Averagesupernova
Science Advisor
Gold Member
- 4,784
- 1,457
So I guess it's been implied, but I'll go over it again. The unit samples each line voltage with respect to the neutral. And you are saying since this is the case, that for instance in a 120/208 volt wye connection with a line to line load the unit will think it is X amperes multiplied by 120 volts twice to obtain the power. But we all know it is only 208 volt multiplied by X amperes. The part you are missing is that the current is out of phase with the voltage in each transformer winding. It leads in one winding and lags in the other. If you do the math you will find this to be the case and true power consumption will work out correctly.