Calculate power consumed by pressure drop
This discussion focuses on calculating the energy consumption of a HVAC Variable Air Volume (VAV) box, specifically how much energy is utilized by 1,000 CFM of 55°F air at a static pressure drop of 0.2" water column (wc). The calculations provided indicate that the energy consumed over one year is approximately 220 kWh, considering a fan efficiency of 65%, which raises the total to about 317 kWh. The discussion also highlights the importance of accounting for motor efficiency, which can reach up to 95% for larger motors and 98% for Variable Frequency Drives (VFDs).
  • Understanding of HVAC systems and components, specifically VAV boxes
  • Basic knowledge of fluid dynamics and pressure drop calculations
  • Familiarity with energy consumption metrics, including watt-hours and kilowatt-hours
  • Knowledge of efficiency ratings for fans and motors in HVAC applications
  • Research HVAC fan efficiency calculations and their impact on energy consumption
  • Learn about the role of Variable Frequency Drives (VFDs) in optimizing motor efficiency
  • Explore pressure drop calculations in duct systems for HVAC applications
  • Investigate energy consumption metrics and how to calculate them for various HVAC configurations
HVAC engineers, energy analysts, and anyone involved in optimizing the performance and efficiency of heating, ventilation, and air conditioning systems.
NotionCommotion
Hello all! I am interested in how much energy a HVAC VAV box consumes. Can anyone help me come up with the following equation? I don't need to know the exact formula, and can assume an uncompressible fluid and/or ideal gas. Been about 20 years since I have done this and am a bit rusty. Thank you
How many watts are utilized by 1,000 CFM of 55 F air at 2" water pressure above atmosphere going through a restriction that results in a static pressure drop of 0.2" wp over a duration of 1 year?
Actually, looks like not watts but watt hours, right?
Do I have this correct?
p=0.2" wc = 50 Pa = 50 n/m^2
Q=1,000 CFM = 0.5 m^3/s
P=p x Q = 25 n-m/s = 25 j/s
For 365 days, E = 788x10^6 j = 220 kw-h
Thanks
That looks reasonable to me.
Thanks
PS. I miss doing this stuff!
Starting in English units, it is:
Dp*CFM/6356=hp
Conversion: 746 watts/hp.
I get 206 kWh. Note also, this doesn't include fan efficiency. For a well operating commercial fan, assume 65%. That puts you up to 317 kWh.
Good point about fan efficiency. What about the motor efficiency? A couple percent?
Larger motors running near full speed get upwards of 95%. A VFD is about 98% efficient. The pulley-drive on a fan, 90-95% efficient.
  • · Replies 45 ·
11K
27K
  • · Replies 48 ·